    ‎05-15-2018 04:30 PM
    Listed in the table below you will find the old DS MUX Device part number with the new MUX Device replacement. Replacement Part Numbers Old DS MUX Devices Description FPE-7039, D7039 DS9331, DS9431R MUX Card D7050-B6 MXB2W MUX Base D7044 MX361 Single Point D7044M MX361M Mini Single Point FMM-7045 MX310 Pull Station FMM-7045D MX310D Dual Action Pull Station D7052 MX363 Dual Point Module D7053 MX46 I/O Input/Output Modules D7050 MX250 MUX Smoke Head D7050TH MX250TH MUX Smoke Head with 135 Heat Sensor  .
    View full article
    ‎05-07-2018 10:22 PM
    Steps to enable a SLC card in slot 2
    View full article
    ‎05-08-2018 04:48 PM
    D125X Keypad is not displaying System Faults
    View full article
    ‎04-06-2023 03:03 PM
    Part numbers FPA-1000, FPA-1000-V2, FPE-1000-NE, FPE-1000-NW, FPR-1000-NF  
    View full article
    ‎05-21-2018 07:50 PM
    Part numbers D192C, D192G
    View full article
    ‎06-01-2018 03:48 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7412G, D9124G, D9412G, D7412GV2, D9124GV2, D9412GV2, D1256
    View full article
    ‎04-06-2023 03:26 PM
    The FLM-325-2i4 is a Single address Dual Input Analog Addressable Module with two inputs used to monitor Normally Open (NO) or Normally Closed (NC) circuits.  If the module is addressed as 010 the First input will display as 010.1 on the panel keypad display, the Second input will display as 010.2 on the panel keypad display. 
    View full article
    ‎04-06-2023 03:13 PM
    Part Numbers, FAD-325 (DUCT Housing without Relay), FAD-325-V2F (DUCT Housing without Relay), FAD-325-R (DUCT Housing with Relay), FAD-325-V2F-R (DUCT Housing with Relay) FML-325-2R4, FML-325-2R4-2A, FML-325-2R4-2AI, FML-325-2R4-8A, FML-325-2R4-8AI, D323DH (DUCT Smoke Head), FAD-325-DH (DUCT Smoke Head), FAD-325-V2F-DH, FPA-1000, FPA-1000-UL, and  FPA-1000-V2.
    View full article
    ‎06-12-2018 10:19 PM
    Part numbers FPD-7024, D7024, DS9400, DS9400I, DS9400M, FPE-7039, D7039, DS9431
    View full article
    ‎08-24-2018 10:18 PM
    How to access the Menu features on the B926F which does not have a Menu button.
    View full article
    ‎07-23-2021 06:52 PM
    Part numbers, D344-RT (Remote Test Plate with Blue Test coil), D307 (Remote Test Plate), D341, D341P, D342, and D342P. How to correct the D344-RT not resetting the D341/D342 duct detector.
    View full article
    ‎04-12-2023 04:49 PM
    Part Numbers FPA-1000, FPA-1000-UL, FPA-1000-V2, D10024A, D10024, D9024, D8024, D328, D328A, D327, D327A, FLM-325-N4, FLM-325-2R4, FLM-3252R4-A2, FLM-325-R24-A8
    View full article
    ‎06-07-2018 04:10 PM
      Issue The D192G panel zone (point) is in trouble and the yellow LED is not on. Solution With the zone/point in trouble and No Yellow LED On there is a wiring fault. One of the following terminals do not have power connected to them. External Power In (EXT PWR IN) and / or Auxiliary Power In (AUX PWR IN). Terminal 1 (AUX PWR IN) 13.75 VDC Terminal 2 (Common) Terminal 3 (Supervised Zone / Point) 2.50 VDC Normal Condition < 1.50 VDC In Trouble condition Terminal 4 (Trigger) 13.75 VDC In Alarm Only Terminal 5 (External Power In) 12 VDC or 24 VDC Depended on needed Output for the NAC's or Power Supply Terminal 6 (Common) This is the Common from an 24 VDC External Power Terminal 7 (Positive Alarm Output) Terminal 8 (Negative Alarm Output) Part number D192G
    View full article
    ‎05-15-2018 04:27 PM
    Mux Card replacement (DS9431, DS9431R, D7039, or FPE-7039) on any of the following panels DS9400, DS9400I, DS9400M, D7024, and FPD-7024.
    View full article
    ‎06-13-2018 10:36 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7412G, D9124G, D9412G, D7412GV2, D9124GV2, D9412GV2, D7412GV3, D9412GV3, D7412GV4, D9412GV4, D9127, D9127T, D9127U, D8127, D8126
    View full article
    ‎06-12-2018 03:19 PM
    Issue One of the zones at the panel is in constant trouble.   Solution   Need to have proper wiring connections.  Check the following: 1. Using 12 Volt Smokes, Terminal 1 goes to Terminal 8 on the panel Switched AUX Power. 2. Make sure D136 relay is installed for Relay C for non G-Series panels. 3. For 24 Volt Smokes, Terminal 1 goes to a D130, and a UL 24 Volt PSU is needed on Terminal 8 on the Panel. Switched AUX Power goes to the D130 to reset the 24 Volt power. 4. Measure the EOL across loop "A" Terminals 7 and 9 of the D125B card. Look for 1.8K Ohms for the D125B on a new install or when adding to an existing install. If replacing a D125 or D125A the EOL would be 1.5K Ohms. 5. Measure the EOL across loop "B" Terminals 6 and 8 of the D125B card. Look for 1.8K Ohms on the D125B card on a new install or when adding to an existing install. If  replacing a D125 or D125A the EOL would be 1.5K Ohms. 6. Measure the Voltage across  Loop "A" Terminal 3 and Terminal 4 on the D125B card. The meter should read 2.5VDC with everything connected. If the reading is 5VDC the loop is Open (not seeing the 1.8K EOL across the last Smoke. If the voltage reading is Less than 1VDC you have a Short on the loop. The short could be a smoke head latched in alarm, bad/dirty smoke head, wiring short, or reversed polarity to one of the smoke heads on the loop. 7. Measure the Voltage across  Loop "B" Terminal 2 and Terminal 4 on the D125B card. The meter should read 2.5VDC with everything connected. If the reading is 5VDC the loop is Open (not seeing the 1.8K EOL across the last Smoke. If the voltage reading is Less than 1VDC you have a Short on the loop. The short could be a smoke head latched in alarm, bad/dirty smoke head, wiring short, or reversed polarity to one of the smoke heads on the loop. To verify the D125B is working correct you can wire the 1.8K Ohm EOL accross termainals 7 & 9 and another 1.8K Ohm EOL accross termainals 6 & 8. The Loop termainals 2 & 3 need to wire to the Positive Side of a 1K Ohm Zone. The EOL for the 1K Ohm zone is built in to the D125B. Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7412G, D9124G, D9412G, D7412GV2, D9124GV2, D9412GV2, D7412GV3, D9412GV3, D7412GV4, D9412GV4, B9512G, B8512G, D125B
    View full article
    ‎05-16-2018 04:20 PM
    Part number FPD-7024, D7024, DS9400, DS9400I, DS9400M, DS9431, D7039, FPE-7039
    View full article
    ‎12-20-2021 05:33 PM
    Part numbers FPD-7024, D7024, DS9400, DS9400I, DS9400M, D7039, FPE-7039, DS9431
    View full article
    ‎05-14-2018 05:14 PM
    *Note: DS9431 MUX was replaced by the D7039, The D7039 was replaced by the FPE-7039
    View full article
    ‎05-15-2018 04:21 PM
    Perform these steps to enable the D7024, FPD-7024, DS9400, DS9400I, and DS9400M for RPS programming via phone line with a compatible RPS modem: Press (0) Enter Program Mode. Enter Pin (Default is 9876). Press (6) Accounts. Press (4) Ring Count. Set Ring Count to (02) #. Press the (*) key two times or until you see PROGRAM MODES. Press (3) System. Press (7) Remote Program. Press (1) Enable. Press the (*) key five times to Exit Program Mode. You need to dial Line 1 on the panel. It is the second line down on the panel (it is NOT the line in the top right). Before connecting with RPS, perform an Auto-Learn with at least one Mux Device connected to the Mux loop, then send your RPS program to the panel. Press (0) Enter Program Mode. Enter Pin (default is 9876). Press (9) Program Mux. Press (4) Auto Program. Press (1) Yes.
    View full article
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist