Perform these steps to enable the D7024, FPD-7024, DS9400, DS9400I, and DS9400M for RPS programming via phone line with a compatible RPS modem: Press (0) Enter Program Mode. Enter Pin (Default is 9876). Press (6) Accounts. Press (4) Ring Count. Set Ring Count to (02) #. Press the (*) key two times or until you see PROGRAM MODES. Press (3) System. Press (7) Remote Program. Press (1) Enable. Press the (*) key five times to Exit Program Mode. You need to dial Line 1 on the panel. It is the second line down on the panel (it is NOT the line in the top right). Before connecting with RPS, perform an Auto-Learn with at least one Mux Device connected to the Mux loop, then send your RPS program to the panel. Press (0) Enter Program Mode. Enter Pin (default is 9876). Press (9) Program Mux. Press (4) Auto Program. Press (1) Yes.
From RPS in the following panels DS9400, DS9400I, DS9400M, D7024, and FPD-7024 you have the option to set Anti-takeover Setting to one of the following. a.)Allow all local programming: All programming items may be accessed from the local keypad. b.) Lock phone/account numbers only: All programming except phone numbers and account numbers may be accessed from the local keypad. c.) Lock all local programming (except Date/Time and all user PINs): Allows only the Date and Time to be set from a local keypad.
Overview
When devices are connected to the Option Bus on the FPD-7024, the bus must be scanned allowing the panel to see the device. After removing devices, such as the DX4020, DX4010V2 or DX4010i, the option bus must be scanned again to complete the removal, or the panel continues to supervise the device resulting in a keypad display: Trouble DX4020 and history event: SYSTRB017.
Issue
After completing programming the panel reports trouble DX4020; history shows SYSTRB017
Solution
After removing the DX4020, DX4010V2 or DX4010i, the option bus must be scanned again to complete the removal or the panel continues to supervise the device.
From the Panel Keypad (not a remote keypad) perform the following steps to update the option bus:
Select 0 for PROGRAMMING and enter the installer code
Select 3 for PROGRAM SYSTEM
Select 4 for OPTION BUS
Select 1 for UPDATE BUS