Use the tool provided when FSM server application is installed, to manage export/import of configurations.
Please note: This tool is only for configuration backup and does not include logs and history.
The FLM-325-2i4 is a Single address Dual Input Analog Addressable Module with two inputs used to monitor Normally Open (NO) or Normally Closed (NC) circuits. If the module is addressed as 010 the First input will display as 010.1 on the panel keypad display, the Second input will display as 010.2 on the panel keypad display.
Issue
What are the proper steps in cleaning a DS200HD smoke head?
Solution
Turn off all electrical power to the detector.
Depress the tab on the two sides of the detector adjacent to the LED, and pull the unit from its base.
Fill three (3) clean buckets each with 1-1/2 gallons normal tap water.
NOTE: De-ionized or distilled water is preferable in areas where hard water with large mineral content is prevalent.
Add one (1) teaspoon of dishwashing liquid (Ivory Dishwashing liquid only) to the first bucket and mix thoroughly, then place the dirty detector into the soapy water until it is completely submerged. Allow the unit to soak for approximately ten (10) minutes, then agitate to insure all dust and dirt is removed.
Remove the unit to the first clean water bucket, submerge detector and agitate for 5-10 seconds to remove all soap residue.
Finally, move unit to the second clean water bucket, and repeat the procedure in step #5. Remove from second bucket, then vigorously (not violently) shake unit to drain all water. Remove unit to dry area and allow to drain and dry by resting unit on its side. Allow unit to dry for a period of 72 hours before use.
Caution:
Air Dry units only.
Do not use any hot air device or attempt to place unit in oven, as this will result in damage to the detector. Also wash and rinse water should be changed every 5-7 units to maximize the results.
A sticker on the front of the B450 indicates proper switch positions for selecting various SDI or Option Bus addresses (see figure 1).
Figure 1 Sticker with address configurations
There are 2 types of FPD-7024 panels. It must first be determined which is in use before selecting the B450 address:
Newer types with firmware version 1.06 and higher. These types are identified by icons on the keypad instead of words (see figure 2).
Older types with firmware version 1.03 and lower. These types are identified by words on the keypad.
Figure 2 Version 1.06 with Icons vs 1.03 with words
Version 1.06 & newer types:
When used as sole communicator or backup to phone line, set the address wheel at 9 for Option Bus address 250.
When used as backup to a primary network communicator, set the address wheel at 6 for Option Bus address 134.
RPS connections require Option Bus address 250. Be sure the address wheel is set at 9 on the network communicator intended for RPS connections (Ethernet is preferred when allowed).
Version 1.03 and older types:
Use Option Bus address 250. Only one network communicator is available on these panel types.