How to troubleshoot Comm Fail when intrusion alarm panels communicate over phone lines.
What would cause a control panel to go into Comm Trouble or Comm Fail?
Issue
Points are faulted but the panel does not react.
Solution
Points must be faulted for 500 milliseconds minimum.
*When using self resetting devices, some do not latch the contact in the faulted position but do show a fault trip via a latched LED.
Issue
On 2000 series panel, point codes are programmed for points between 9 and 24. When programmed points are tested the keypad reads "PT(#) PT DISABLED (where # is the number of the point being tested).
Solution
Pt text (Point Text) was never changed from default that read "PT(#) PT DISABLED".
Issue
What are the enviromental considerations for the proper operation of the Bosch control/communicators?
Solution
Indoor Dry.
Relative Humidity 5% to 85% noncondensing at +86 degrees Fahrenheit (+30 degrees Celsius).
Operating temperature would be +32 degrees Fahrenheit to +120 degrees Fahrenheit ( 0 degrees Celsius to 49 degrees Celsius ).
Issue
Does the D2112Command Centerbuzz discontinue after AC power is restored?
Solution
Yes. The Command Centertrouble buzz will timeout after 30 to 45 seconds following restoration of AC power.
Overview: Firmware revision 2.20 and higher limit errors when keypad programming a D2212 panel for D208 point expansion.
Issue
Why does the D2212 panel not allow keypad programming for a D208 point expander?
Solution
Before firmware revision 2.20, it was NOT possible to program the D2212 for a D208 Point Expander using keypad programming. Panels before firmware version 2.20 should be programmed with the D5200 handheld programmer or RAMIV/RPS download software.
Firmware revision 2.20 and above CAN be programmed via the keypad.
Issue
If the Central Station receives a signal in 4 x 2 format from a D2112 panel, how can that signal be deciphered using the programmed settings in the panel ?
Solution
The report code will consist of data digit 1 and data digit 2. When sending signals in Pulse, the first digit of the reported signal must be set to a particular report group in panel programming. The second digit will contain the point number or user number or event number that relates to digit one.
The chart below shows the Description of what the second digit of a reported code would be if the first digit were programmed as show below. NOTE: The first digit could be any selection 0-9 or B-F for any of the report groups.
To decipher the reported code: If using the D5200, look in programming under Receiver Format and RPT Groups for Pulse. The number entered beside the Report Group is what will come in as the first reported digit. Using the chart below, the point number or user number or event number that pertains to the second digit is described.
In remote programming, view the report section of the program to determine the report group programmed for Digit one. Using the chart below, the point number or user number or event number that pertains to the second digit is described.