How to correct the D132A supervision point not showing normal circuit status.
Cannot get the onboard point from the D132A module to show normal circuit status.
D132A,D4412,D6412,DS7220,DS7240,D2212
Issue
Unable to enter into program mode whether using a passcode or shorting out the solder pins, and the panel is not locked out of programming mode.
Solution
Make sure the panel does not have a ground fault issue. The best way to tell is to check the following:
Take a voltage reading from aux power positive to Earth ground.
The voltage should read - 6.7VDC.
If the voltage is lower or higher than -6.7VDC, a ground fault is present.
The panel may indicated this trouble if it is turned on.
If the voltage is 0VDC - the ground fault condition is on the positive side of the panel
If the voltage is 13 VDC then the ground fault is on the negative side of the panel.
Leave the volt meter accross the terminal and start disconnecting wires until the voltage goes to -6.7VDC
Issue
Unable to use Command 00 function. When CMD 00 is entered, keypad reads 'SYSTEM COMMAND' or 'INVALID KEYS'.
Solution
Un-Bypassing points on the D7112 panel must be done by using the FUNCTION Menu. Access the Function menu by pressing 'Enter' at the idle disarmed text. Press Next repeatedly until Function Menu displays. To access the UNBYPASS screen press enter on Function menu and Next until UNBYPASS displays. Display will read ENTER POINT NUMBER, enter the point number to be bypassed and press Enter. Display will read the text for the point, press enter again and screen will read POINT UNBYPASSED.
Issue
What are the steps on setting the panel time for the DS7100?
Solution
Enter in a valid master code # 0,7
Enter 01, then enter the time ( 24 hr. format ) then #