AC Fail/Res Rpt
Default: No
Selections: Yes/No
Parameter Description: AC Power Supervision reports are sent to the central station and local printer at the time programmed for AC Fail Time.
IMPORTANT: To comply with NFPA standards and UL 864 requirements for Commercial Fire Systems, program this item NO and program AC Tag Along as YES.
Parameter Options
Yes: Send AC Fail and AC Restoral reports.
No: Do not send AC Fail and AC Restoral reports.
Programming Instructions
D5200 Programming
1) Receive copy of 9000MAIN
2) Enter group PANEL WIDE PARAMETER
3) Enter group Power Supervision
4) Fail/Res Rpt Yes/No (SPACE bar to change)
*Must press ENTER for each prompt entry
5) Send Load to panel
Use the Menu function ‘MASER ARM’ to arm either selected areas or all areas that the user has authority in, which are in the scope of the keypad. Previously armed areas remain armed while the remaining disarmed will arm.
For example, if a panel uses areas 1-8 and:
The keypad has Panel Wide Scope and the user has authority only in areas 1, 2, 3 & 4, then only areas 1, 2, 3 & 4 will Master Arm.
If the keypad has Custom Scope in areas 1 & 2 user has authority in areas 1, 2, 3 & 4, then only areas 1 & 2 will arm.
Use the Menu function ‘MASER ARM’:
Access the keypad Menus from the keypad.
Press the NEXT key until the MASTER ARM ? function is displayed and select [ENTER].
Enter a valid passcode and press [ENTER].
The display shows MASTER ARM ALL ?, select [ENTER].
The command center displays ARMING X,X,X,X… where X= the available and authorized areas to arm.
Issue
An FA400 receiver that is disconnected will not force the keypad to display a missing message.
Solution
If two FA400 receivers are being used on the same D8125INV, the "Receiver Missing" message will not display if only one of the receivers is disconnected.
How to interpret the panel executing Skeds 41-56 when only skeds 1-40 are available.
Why does the panel shows Skeds between 41 and 56 executed when only skeds 1-40 are available in programming?
How to determine D928 compatibility with D7212 panel types.
After changing the setting "Two Phone Lines" to Yes then unlatching and relatching the Reset Pin, it is changed back to No.
The keypad will display ‘Command Disabled’ when the Menu key is pressed for one of the following reasons.
If the menu item # 1 in the function list is set with a function 0 and marked yes for any Command Center.
If all of the Functions for the Command Center are selected as No (disabled).
To prevent the keypad from displaying ‘Command Disabled’ after selecting Menu;
Select a non-zero value for the Function # of Menu Item 1.
Ensure that at least one of the Menu Items intended for use are set as Yes.
How to activate multiple auxiliary relays on Area Wide or Panel Wide Events.
Programming Area Wide or Panel Wide Relays will only allow a single relay entry. Use an auxiliary relay such as the D130, D133 or D134 when multiple relays are needed to energize on a panel event.
How to address SDI2 devices without causing address conflicts.
Can different types of SDI2 devices use the same address setting?
B810, RFRP-A, B820, B208, B308, B420, B426, B520, B920, B921C, B930, B942.