How to determine D928 compatibility with D7212 panel types.
After changing the setting "Two Phone Lines" to Yes then unlatching and relatching the Reset Pin, it is changed back to No.
How to correct point 1 on a D4412 or D6412 will not restore even when using the programmed EOL.
Point 1 on the D4412 or D6412 will not restore even after strapping out with the EOL selected in Global Point Configuration.
How to correct the Panel reporting Extra Points on Zones 1-8.
The keypad is displaying trouble due to extra point on an onboard zone(1-8).
5800C,5800G,5900C,5900G
How to configure Swinger Shunt to prevent points from automatically bypassing after only 1 alarm.
Why does the panel zone generate 1 Alarm and then goes into Swinger Bypass?
D4412,D6412,DS7220,DS7240
Issue
Trouble connecting to the D4412 with RPS / RAM IV using the DX4010i.
What dip switches need to be set to make the DX4010i connect to the panel?
What type of cable is needed between the DX4010i and the Laptop or PC?
Solution
RAMIV / RPS needs to be revision 3.6 or higher.
Set the address 0 (Installer's mode) Dip Switches 6 and 8 in the off postion on the DX4010i.
Use a NULL cable to connect the DX4010i to the Laptop or PC.
For remote programming connection, use the RJ-16 to molex connector to the Aux / Data header.
Lock the Installer or Reset Pin on the panel.
In the RSP/ RAMIV Connection screen change the connection type from MODEM to ENHANCED DIRECT, then click connect.
*If connected to a D4412 panel and the address is set wrong on the DX4010i then a message of "INVALID RAM PASSCODE" may be generated.
Issue
Symptom
What would cause the programmer to display ( Plug in 7112) when you press send or receiver
Diagnosis
The programmer is not correctly connected to the D7112.
Solution
Verify that the data/power cord is plugged securely in the programmer port J4, on the D7112.
Verify that the data/power cord is plugged securely into the communicator port on the D5200 programmer
Check each conductor in the data/power cord for continuity
Part numbers D7112, D5200
How to initiate a programmed test time on 2000 Series control panels.
Does the D2212 Timer Test Need to be Initiated from the Keypad?
D2812,D220A (8 led),D2412,D2212,D222A LCD,D223A LCD,D220A,D222,D223