How to work with the D6112 Battery Discharge and Recharge voltage schedule.
When does the D6112 report Low Battery?
When does the D6112 report Low Battery Restoral?
Issue
What is RPS Call Back?
Solution
RPS Call Back
Default setting is No.
Selections are Yes or No
Parameter Description
Using this function allows the control panel, after it has verified the RPS passcode, to provide an additional level of security by hanging up and dialing the RPS phone number to call RPS at the central station prior to allowing any upload or download.
Important: When using the RPS Callback function, enter a "C" as the last digit in the RPS phone number if DTMF dialing is used.
Parameter Options
Yes: When the control panel hears the proper RPS passcode, it hangs up the phone, seizes the phone line, then dials the programmed RPS phone number (see RPS Ph ). This ensures that only the control panel communicates with the RPS PC connected to the dialed phone number.
No: The RPS session is initiated immediately; no call back is required. The control panel engages in RPS sessions when called from any phone number and a proper RPS passcode is identified.
On a D720, why are all the zone lights flashing?
D9412,D7412,D7212,D9412G,D7412G,D7212G,D9412GV2,D7412GV2,D7212GV2,D9412GV3,D7412GV3,D7212GV3,D9412GV4,D7412GV4,D7212GV4,D7212B,D7212B1,D9112,D9112B,D9112B1
RPS connection to the IP of the Cellular Card when using a B450 on any the following panels, GV2 with Firmare 7.06 and higher, GV3 Firmware 8.0x and the FPD-7024 with Firmware 1.03 and higher.
The Standby (Reset) pin is not locked down. The panel 12V backup battery is low or missing. Using the wrong product handler, for example, using 2112 instead of 2212. Too much Current Draw on panel. Disconnect devices from Aux Power and try again. Noise or interference on the keypad Data Bus. Disconnect all wires on the panel data terminals. Not enough free memory in the D5200 Programmer. There should be 60K free memory. Refer to KB article: How to Operate the D5200 Hand Held Programmer. The 2212 handler may be corrupted in the D5200. Delete the 2212 handler and re-download it. Refer to KB article: How to Operate the D5200 Hand Held Programmer. Low batteries in the D5200. Replace batteries using 4 C cells. Trying to program a panel that is not powered up The programming cord is not securely connected to the panel programming port or may be damaged. The DX4010V2 comes with a cord with a 4-pin Molex connector on one end and phone connector on other end. This cable may work as a substitute.
Issue
Trouble tones will clear and then return one hour later.
Solution
RF Sensor Low Battery
With earlier revisions of panel firmware, users could silence a low RF fire sensor battery trouble indefinitely. With revision 3.03 (or later), the panel restarts the trouble sounder at the keypad within four hours if the low battery in the fire sensor is not replaced.
This article describes how to correct a situation where text in the main page of RPS appears normal but text in the panel account programming page is much smaller.
Issue
The FA113 will not arm the panel if it was disarmed from the keypad and will not disarm if panel was armed from the keypad
Solution
Used as an arm/disarm device, the FA113 is configured to panel zone 74 or 194. Pressing the FA113 Off button sends an OPEN signal to the control panel and pressing the On button sends a NORMAL signal to the control panel.
The area should be both Armed and Disarmed by the FA113 for it to function correctly. When the arming state is changed by the FA113, then by another means, the FA113 becomes unable to detect the current armed state of the area and will not respond to the keys pressed.
Correct settings for FA113:
The transition of the state of point 74 is what causes the area to arm or disarm. • Mode in the D8125INV is set to 4. • Keyswitch Maintained point (Point Type 4) with Point Response 2, is required for the FA113. • Area will arm with a transition from open to normal on point 74. • Area will disarm with a transition from normal to open on point 74. The FA113 is also used for panic on point 75 (7412G) and point 195 (9412G).
Issue
The instructions do not show how to interface the D169 to the D6412.
Solution
Voice Verification: Allows the panel to control a D169 2-way Voice Verification Module. The D169 allows the central station personnel to verify alarms with a two-way voice session with the premises. The premises phone line runs from the panel to the D169 and then to the premises phones. There are two other module connections to the panel: the programmable relay output (-12 VDC) programmed with the Voice Request output function (2,10), and a point (zone) programmed as a Voice Active point. The panel must also have one or more points with the Voice Verification option selected in the point index. When a point with Voice Verification generates an alarm event:
The panel transmits the alarm report to the receiver at the central station.
When the central station receiver acknowledges the report, the panel activates the Voice Request output function and starts a 30-second report delay time. All reports are delayed. The D169 has 30 seconds to start a two-way voice session.
An operator at the central station picks up the phone line from the receiver with a DTMF telephone and presses [2].
At the premises, the D169 picked up the phone line when the panel activated the Voice Request output function. When it hears the DTMF tone from the operator pressing [2], it begins a two-way voice session by first shorting the panel’s Voice Active point.
When the Voice Active point is shorted, the panel silences the non-fire alarm output (sets the Bell Timer to zero). Only the user can silence a fire alarm output.
As long as the Voice Active point is shorted, the panel continues to keep reports buffered.
The D169 ends the voice session by removing the short from the voice active point. The panel resets the bell time and Alarm Event Abort Window (assuming a user at the premises did not change the arming state of the panel during the voice session). Normal reporting (communication) resumes.
Hardware Configuration
1.) J1 cable to the D6412
Brown to the negative out put
Green to the Voice active zone one the panel
Blue to the alarm out put if used
White not used
Red 12volts positive
Black panel common
2.) J3 leave a default with A, and D jumped out.
Need to follow instruction on the D169 for siren wiring, and operating instructions of the D169.