    ‎05-22-2018 03:56 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7412G, D9124G, D9412G, D7412GV2, D9124GV2, D9412GV2, D7412GV3, D9412GV3, D7412GV4, D9412GV4,
    View full article
    ‎06-18-2018 04:35 PM
    How to interpret Missing Command 7 or Command 9. Why are points 72 or 136 showing as MISSING in view point status? Why are points 128 or 248 showing as MISSING in view point status? D7212B,D7212B1,D9112B,D9112B1
    View full article
    ‎06-19-2018 10:40 PM
    Issue CMD40 System Trouble Report Codes Display -  COMMAND 40 Solution Keying COMMAND - 4 - 0 at the Command Center will replace the display of zone status on the four left indicator lights with a trouble report code.  If applicable, a second trouble report can be displayed by keying in another COMMAND 40 (the maximum number of troubles held in the buffer is two).  If no indicators light on the second COMMAND 40 entry, there is only one cause for each trouble report. After the panel is disabled/restarted, powered cycled, or serviced for the indicated system troubles, clear the system trouble memory by entering COMMAND 40 until no troubles are displayed.  Press any key to exit COMMAND 40 since it is not automatically exited upon alarm or trouble condition. Alarms and troubles will continute to report to the central station unabated. 2|4 : D5100 Communication Error / bad connection to programmer 1     : Faulted Zone 2     : Command Center Communication Err / noisy environment or wiring issue 1|2: Communication Failure / unable to communicate with central station 3     : RJ Jack Supervision / phone cord unplugged or wired incorrectly 1|3:   Aux Power Supervision / possible short on aux device or wiring 2|3:   AC Power Fail / Check transformer power and/or wiring 1|2|3:Battery Supervision / low or failing battery 4    :  Command Center Fault / Check wiring and/or programming 1|4:    Internal Hardware Fault / main system board failure 1|2|4: Missing Serial Device / check keypads and/or expander 3|4:    Device Programming Err / keypad or expander does not match programming. 1|3|4:  Internal Sofwtare Err / internal memory failure 2|3|4:  Checksum Fail / EEPROM Failure 1|2|3|4: System ROM Failure / Internal ROM Failure 
    View full article
    ‎06-17-2018 08:27 PM
    Issue Can I change the user text on a 7000-9000 series panel via the keypad? Solution You may only change the users name via a keypad if you have a D1260 keypad.  Follow the steps below to make the changes. >Command 56 then Passcode >Choose the user number and press ENTER >Press the soft key menu item CONTINUE >Press the soft key menu item NAME >Follow the soft key menu to move left/right and to change the characters in the name. >After you done with the modifications press the soft key menu item CONTINUE >If this is correct you press the soft key menu item YES >If it is not correct then press the soft key menu item NO After you have completed your task press the soft key menu item EXIT D1260 Compatible Control Panels • B9512G/B9512G-E • B8512G/B8512G-E • D9412GV4/D7412GV4/D7212GV41 • D9412GV3/D7412GV3/D7212GV31 • D9412GV2/D7412GV2/D7212GV21 • D9412G/D7412G/D7212G • D9412, D7412, D7212, and D9112 with firmware versions 6.40 or higher
    View full article
    ‎06-05-2018 07:39 PM
    How to correct the issue when users cannot clear fire alarms from the panel.
    View full article
    ‎06-22-2018 08:08 PM
    How to correct zones not showing faulted in disarm state on of D4112/D6112 panel keypad. D6112,D4112,D420A (6 led),D620,D636A.
    View full article
    ‎06-18-2018 06:49 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7412G, D7412G, D9124G, D9412G, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7412GV3,D7412GV3, D9412GV3, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G,
    View full article
    ‎05-22-2018 03:56 PM
    Issue Installing a used CPU with unknown programming. Solution CPU can have the RAM cleared. Procedure: * This should be done with the CPU off the panel. With the CPU removed off the panel, remove the shroud; find CR2 and U8 on the circuit board. Place a 3 sec short across the banded end of CR2 and the center pin of U8. This will erase ALL Ram memory. Part numbers D8105, D8107, D8112, D8112A, D8112E, D8112E1, D8112G, D8112G1, D8112G2
    View full article
    ‎05-23-2018 03:51 PM
    The keypad is giving a trouble tone after a CMD 47 is entered to reset the smoke detectors. D7412G,D9412G,D7212,D7212B,D7212B1,D7212G,D7412,D9112,D9112B,D9112B1,D9412,D1255,D1260,D720,D7412GV2,D9412GV2,D7212GV2,D9412GV3,D7412GV3,D7212GV3,D9412GV4,D7412GV4,D7212GV4,B9512G,B8512G,B920,B930,B942
    View full article
    ‎07-16-2018 05:28 PM
    How to correct Bypass Reports Logging and/or Printing but not reporting to Central Station.D4412,D6412
    View full article
    ‎06-15-2018 02:52 PM
    Issue D7112 Panel battery will not hold a charge. Solution A slow flashing (1 sec on, 1 sec off) yellow LED with the green CPU LED off indicates a power supply overload condition.  The panel detects the battery as missing and the power supply cannot meet the power demand of the devices on the panel. The panel is shut down.
    View full article
    ‎05-25-2018 04:47 PM
    The D1252 keypad is displaying jumping stars accross the LCD screen. What does this mean? D8124,D8112E1,D8112G1,D8112G2,D1251AF,D1252,D1252A
    View full article
    ‎07-11-2018 06:37 PM
    Issue When attempting to connect to a DS7080iP-32 or DS7400Xi Ver4+ panel in WDSRP 2, Direct Connect does not appear as an option when Communicate is pressed. Solution WDSRP has not been set up to use Direct Connect function. Go to Utilities and Preferences, check Direct Serial Connect and press OK. Go back to Communicate screen and Direct Connect will appear.
    View full article
    ‎06-14-2018 06:22 PM
    Issue How does the phone line monitor for the DS7100 operate?   Solution   If the monitor detects a phone line fault for more than 50 seconds, the power LED will begin to flash.  If the audible output has been enabled in line 89, the keypad sounder will pulse every ten seconds if the control is disarmed. If the panel is armed, the siren output will activate. To ascertain if the trouble condition is indeed a phone line failure, enter # 87 at the keypad. The display will indicate "Communication Failure". If the "System Trouble Report" (line 51) is programmed the system will try to send this report. A phone line failure may be caused by: A cut or missing phone line. A reversed connection (Tip, and Ring Reversed) A miswired jack To clear the error; Determine the cause of the failure and eliminate the cause. After eliminating the cause of the failure, wait at least ten seconds. The error will clear if the problem has been eliminated and the LED will stop flashing provided a failure has not occurred on the central station phone numbers. If a failure has occurred at the central station restore by entering # 87 * at the keypad.
    View full article
    ‎05-17-2018 09:13 PM
    The central station is only getting the last three digits of a 4 digit account #. How is the full 4 digit account # reporting enabled at the receiver? D8112G2
    View full article
    ‎06-29-2018 03:30 PM
    Issue What scope should be used when programming the D720 keypad?   Solution   The D720 keypad must be programmed AREA WIDE scope only. Account or Panel Wide scopes are not supported by this keypad.   Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4, D720
    View full article
    ‎06-18-2018 09:57 PM
    How to view System Troubles on the DS7240/DS7220. DS7240,DS7220,DS7445I,DS7447I
    View full article
    ‎05-17-2018 09:14 PM
    How is a point index set up for an Interior Follower on a B panel and on a 7000/9000 series panel? D9412, D9412G, D7412G, D7212, D7212B, D7212B1, D7212G, D7412, D9112, D9112B, D9112B1, 5800B, 5800B1, 5900B1, 5900B, 5800C, 5900C, 5900G
    View full article
    ‎06-20-2018 07:29 PM
    How to force the DS7240/DS7220 to answer remote programming software. DS7240,DS7220,DS7445I,DS7447I
    View full article
    ‎06-18-2018 10:58 PM
    How to add a passcode on the 2000 Series panel using a Text Keypad. D2212, D222A LCD, D223A LCD, D222,D223, D2412,D2812
    View full article
    Top Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist