How to interpret the panel executing Skeds 18-49 when only skeds 1-17are available.
D7212B,D9112B,D9112B1,D7212B1
Why does the panel show skeds between 18-49 executing when the panel only has skeds 1-17 available in programming?
How to interpret the panel executing Skeds 41-56 when only skeds 1-40 are available.
Why does the panel shows Skeds between 41 and 56 executed when only skeds 1-40 are available in programming?
How to program the D8112 panel to report AC Restoral Reports.
Central Station Receiving AC Fail Reports but not AC Restoral Reports.
D8112E1,D8112G1,D8112A,D8112G2.
How to determine D928 compatibility with D7212 panel types.
After changing the setting "Two Phone Lines" to Yes then unlatching and relatching the Reset Pin, it is changed back to No.
How to correct point 1 on a D4412 or D6412 will not restore even when using the programmed EOL.
Point 1 on the D4412 or D6412 will not restore even after strapping out with the EOL selected in Global Point Configuration.
How to correct the Panel reporting Extra Points on Zones 1-8.
The keypad is displaying trouble due to extra point on an onboard zone(1-8).
5800C,5800G,5900C,5900G
The keypad will display ‘Command Disabled’ when the Menu key is pressed for one of the following reasons.
If the menu item # 1 in the function list is set with a function 0 and marked yes for any Command Center.
If all of the Functions for the Command Center are selected as No (disabled).
To prevent the keypad from displaying ‘Command Disabled’ after selecting Menu;
Select a non-zero value for the Function # of Menu Item 1.
Ensure that at least one of the Menu Items intended for use are set as Yes.
How to activate multiple auxiliary relays on Area Wide or Panel Wide Events.
Programming Area Wide or Panel Wide Relays will only allow a single relay entry. Use an auxiliary relay such as the D130, D133 or D134 when multiple relays are needed to energize on a panel event.