Bosch Building Technologies

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 

    Security: Intrusion

    Sort by:
    ‎05-22-2018 03:41 PM
    How to use the D9210B & D9210C on the same panel.
    View full article
    ‎06-25-2018 04:21 PM
    Issue How is point expansion configured, addressed and wired on the D6112 panel? Solution Connections: 1.) Install the First Device to the D6112 control by connecting one of the two White leads to terminal 11 (Data- first device). The Black lead will land on terminal 14 (common) and the Red on terminal 15 (+ 12Vdc). This device will be programmed as DEVICE 1. 2.) Install the Second Device to the D6112 control by connecting one of its White leads to the remaining White lead from Device 1. The Black and Red leads of the second device will connect to Common and +12Vdc respectively. This device will be programmed as DEVICE 2. 3.) Each additional device will be installed by connecting its White wire to the previous device remaining white wire until the last device. The remaining White wire on the last device will connect to the D6112 control terminal 13 (Data- last device). Programming: 1.) Go to the Devices Module part of the D6112 handler and on line 4.1 Device#, select 1 for the first device. a) On line 2 D1 Model, select the device model code (1=D610/611, 2=D620/D626, 3=D630/D636A, 4=D640) that pertains to the first device. 2.) Continue by selecting 2 on line 4.1 Device# for the second device and on line 4.2 D1 Model, enter that device model code. Continue until all devices are programmed. 3.) Address the points according to the device they are expanded off of. The zone location is comprised of the Device model code and the zone. The zones are identified by letter starting with A for the first zone and counting up alphabetically. a) Onboard zones 1-8 use a device code of 0 and are addressed as 0A-0H. b) Zones 9 and up would be addressed 1A, 1B and so on. Note: It is not required that zones 1-16 be located on any particular device or in any particular order. It is advisable that the system be laid out in a logical order for future reference.
    View full article
    ‎05-22-2018 03:44 PM
    What zone code is needed on a D6112 and the D4112 for a D279 sub zone control D6112,D268,D279,D279A
    View full article
    ‎06-28-2018 07:48 PM
    How to determine correct wiring with between the DS7420i and different DS7400 panel types. Is the wiring configuration between the DS7420i and DS7400 panel different than with the DS7400Xi? DS7400,DS7400X,DS7400Xi,DS7420i.
    View full article
    ‎05-31-2018 03:44 PM
    How to determine the max distance the DX2010 can be remote located from the control panel. This distance is determined by whether or not the DX2010 is supplying auxiliary power to devices. The DX2010 has the capacity to provide 12 VDC at up to 100 mA from the Aux Output terminals to power external devices such as motion detectors.
    View full article
    ‎06-08-2018 03:51 PM
    How to connect 4-wire Smoke Detectors to D2000 Series Control Panels. D2212B, D2212BE, D2412U, D2412UE, D2812
    View full article
    ‎07-03-2018 05:22 PM
    Part numbers D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4,
    View full article
    ‎06-19-2018 02:46 PM
    How to determine how long the loop wiring can be or how many devices can be connected to a D9127. D9127U,D9127T,D8125
    View full article
    ‎07-26-2018 03:25 PM
    Issue How far can the D9131A be installed remoted from the control panel?   Solution   The D9131A can be installed a maximum of 1000 ft. (305m) from the panel using 22 AWG solid copper wire.            
    View full article
    ‎06-07-2018 06:38 PM
    How to determine which points are available for programming using the D8125MUX.  D8125MUX, DS7457, DS7457I, DS7457IF, DS7460, DS7460I, DS7461I, DS7465, DS7465I, DS7052, DS7051, D7050, D7050-BB, MX835, MX934, MX794Z, MX250, MXB2W, D5060.
    View full article
    ‎06-20-2018 05:28 PM
     Can the D125B be Used to Power 2 Wire Smokes on the D7112? Yes, see technogram number (73-06116-000-C) 1993 (attached). Listings and Approvals Underwriters Laboratories lists the D7112 ControVCommunicator as a Digital Alarm Communicator Transmitter (DACT) for: NFPA 71 Central Station, NFPA 72 Chapter 6 Local, NFPA 72 Chapter 8 Remote Station, NFPA 74 Household Fire Warning. The D7112 also has the following Approvals: CSFM and NYC-MEA (formerly NYC-BSA).
    View full article
    ‎05-24-2018 04:07 PM
    How to correct the keypad response No RF Module when adding Inovonics RF Points.
    View full article
    ‎07-27-2018 02:34 PM
    Issue When programming the D279 keypad point index on the 7000/9000, G, GV2, & GV3 series panels, how should the type and response be programmed?   Solution   Program a type 7 for D279 (O/C Non-Priority): The D279 provides point arming and disarming independent of the area arm state. A non-priority D279 point arm state does not affect the area arm state. Point Response must be programmed 1. Program type 8 for D279 (O/C Priority): The D279 provides point arming and disarming independent of the area arm state. A priority D279 point must be armed before an area can be armed. Program Point Response as 2.
    View full article
    ‎05-31-2018 04:30 PM
    How to determine if the D5360 is compatible with the GV3 panel.
    View full article
    ‎06-29-2018 06:13 PM
    Issue Trouble connecting to the D4412 with RPS / RAM IV using the DX4010i. What dip switches need to be set to make the DX4010i connect to the panel? What type of cable is needed between the DX4010i and the Laptop or PC? Solution RAMIV / RPS needs to be revision 3.6 or higher. Set the address 0 (Installer's mode) Dip Switches 6 and 8 in the off postion on the DX4010i. Use a NULL cable to connect the DX4010i to the Laptop or PC. For remote programming connection, use the RJ-16 to molex connector to the Aux / Data header. Lock the Installer or Reset Pin on the panel. In the RSP/ RAMIV Connection screen change the connection type from MODEM to ENHANCED DIRECT, then click connect. *If connected to a D4412 panel and the address is set wrong on the DX4010i then a message of "INVALID RAM PASSCODE" may be generated.
    View full article
    ‎05-23-2018 08:38 PM
    Program configuration of a DS7432 module on a D8125 Mux system D9412,D7412,D7212,D9412G,D7412G,D7212G,D9412GV2,D7412GV2,D7212GV2,D9412GV3,D7412GV3,D7212GV3,D9412GV4,D7412GV4,D7212GV4,D8125 MUX
    View full article
    ‎06-29-2018 08:31 PM
    How to set the test report time on the 190 Test Report Timer module for the 4012/8012 panel. D4012,D8012
    View full article
    ‎05-24-2018 04:08 PM
    What EOL resistor is needed on Loops A and B of a D125B module? D125B
    View full article
    ‎05-22-2018 04:05 PM
    Will the D8223-P reader work with the D7412G or the D9412G? D9210B,D8223-P,D8229,D8223
    View full article
    ‎06-15-2018 03:05 PM
    Overview The Bosch Security Systems D221 Answering Machine Disconnect Module allows you to remotely disconnect an answering machine that shares a phone line with a Bosch Security Systems control panel. When the answering machine disconnects the phone line is available to the control/communicator for remote programming (RPS) functions. A Touch-tone® telephone at the RAM site is required to perform the disconnect procedure. The D221 can be installed with an existing modular telephone jack or be a replacement for an RJ-11 jack.   Issue   What activates the module to disconnect the answering machine?   Solution   From a touch tone phone call the phone line, let the answering machine answer the line. The # key or the 8 key will activate the module. 1) module white jumper cut = # key 2) module black jumper cut = 8 key **Note: The RAM session is not affected when the D221 restores the phone line to the answering machine. Some answering machines record tones generated during the RAM session. If the D221 Module is used with an integrated telephone/ answering machine device, pressing the activation key ([#] or [8]) during normal use may activate the D221 and disconnect the device for 3 to 5 minutes.
    View full article
    Top Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist