How to prepare for the D6600 upgrade from version 1 to version 2 firmware.
What to be aware of when upgrading the D6600 receiver from version 1 toversion 2 firmware.
D6600, D6200, D6640, D6641
How to determine the values to enter for the Poll Rate and Ack Wait Time.
Note: The calculation described is only be required on legacy control panels. The B8512G/B9512G and GV4 types only need a Receiver Supervision Time selection. The Poll Rate, Ack Wait and Retry count will automatically populate.
The formula for determining Poll Rate and Ack Wait Time is as follows:
Panel setting: Poll Rate + Ack Wait + ( Retry Count X Ack Wait)
Receiver setting: Panel Poll + Ack Wait
Panel setting = Receiver setting
Example: Panel Setting: Poll Rate = 240; Ack Wait = 10; Retry Count = 5 Panel setting: 240+10+ (5 X 10) = 300
Receiver Settings: Poll = 240; Ack = 60 Receiver setting: 240 + 60 = 300
300 = 300 Refer to the the following site for more information on setting up Conettix Devices
www.conettix.com/Downloads.aspx
How to address SDI2 devices without causing address conflicts.
Can different types of SDI2 devices use the same address setting?
B810, RFRP-A, B820, B208, B308, B420, B426, B520, B920, B921C, B930, B942.
The B8512G and B9512G have slots for two B430 Plug-in Telephone Communicators to provide redundant telephone connections. Upon power up the panel uses the B430 in the Mod-1 slot until a Test Report is initiated or when the panel phone supervision declares the line currently in use as failed. B430, B8512G, B9512G