Bosch Building Technologies

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 

    Security: Intrusion

    Sort by:
    ‎07-02-2018 10:16 PM
    Issue What are  the proper steps to default a DS7100?   Solution   Enter program mode with a valid installers code #0 ( 98765 #0 ) is the default code. Or press and hold the S1 switch for 6 seconds. Enter address 839# Then press the S1 switch for 6 seconds.   Warning: Defaulting the DS7100 will erase all programming and user data in the system resulting in a system that needs to be reprogrammed. Notice: This panal is equipped with Anti-Takeover Protection; all or part of the programmming may be locked so the program cannot be changed should someone attempt to take over the account.
    View full article
    ‎07-02-2018 10:13 PM
    Issue What are the steps to default a DS7090 or DS7090i?   Solution   To set panel back to factory default perform the following: Caution - This will erase all programming except for the phone numbers. What may prevent the panel from being set to factory default is a security feature called anti-takeover. If this is enabled the panel will not be able to be set back to factory default Enter into program mode by the installer code # 0 ( 98765 # 0 ) is the default code, or short the little silver dots next to the last zone on the panel for 4 seconds with a jumper wire. ** Enter 839#, the beeper should sound for steady. Short the same 2 pins, and the panel should be back to factory default. ** When the step is followed and a 3-beep error tone is generated while after 839# is entered. This panel is lock and will need to be reset at Bosch Security System for a fee. Contact our repair department a 800-289-0096 Ex 4220 M - F 8 a.m. - 5 p.m. EST
    View full article
    ‎07-02-2018 09:03 PM
    Issue Bell output only activates for 30 seconds even though it is programmed for 99 minutes. Solution When the fire bell time (address 0195 in version 3, address 4032 in version 4) or burglary bell time (address 0196 in version 3, address 4033 in version 4) is set to 99 for a DS7400Xi version 3 or 4 this sets the bell cutoff time to 30 seconds. For indefinite bell output then these programming addresses should be set to 00.  For 98 minutes of bell output these should be set to 98. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎07-02-2018 04:17 PM
    Issue Can not get some of the functions to work on the command center. Overveiw: Some functions require you to enter single partition mode when using a master keypad. Soultion The following command require that you are in single partition mode when entering from a master keypad. ( valid code ## ) History read-back Chime mode Checking zone status Checking zone troubles status Bypassing zones      Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7447, DS745, DS7447E,  
    View full article
    ‎07-02-2018 04:07 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎07-02-2018 03:19 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7447, DS7447E
    View full article
    ‎06-29-2018 06:56 PM
    Issue What is the dual phone line monitor module for the D7112?   Solution   The D728 would be the dual phone line monitor module for the D7112 panel.
    View full article
    ‎06-29-2018 06:13 PM
    Issue Trouble connecting to the D4412 with RPS / RAM IV using the DX4010i. What dip switches need to be set to make the DX4010i connect to the panel? What type of cable is needed between the DX4010i and the Laptop or PC? Solution RAMIV / RPS needs to be revision 3.6 or higher. Set the address 0 (Installer's mode) Dip Switches 6 and 8 in the off postion on the DX4010i. Use a NULL cable to connect the DX4010i to the Laptop or PC. For remote programming connection, use the RJ-16 to molex connector to the Aux / Data header. Lock the Installer or Reset Pin on the panel. In the RSP/ RAMIV Connection screen change the connection type from MODEM to ENHANCED DIRECT, then click connect. *If connected to a D4412 panel and the address is set wrong on the DX4010i then a message of "INVALID RAM PASSCODE" may be generated.
    View full article
    ‎06-29-2018 05:50 PM
      Issue Symptom The keypad displays Oct. Relay Fault. Probable Cause The octal relay module ( DS7488 ) is defective or the wiring to the module is defective. There is not a DS7488 or a DS7488 has been removed from the system. Solution Check the wiring to the module. Enter the programming mode. This will rescan the options bus and clear the problem. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,  DS7488
    View full article
    ‎06-29-2018 05:43 PM
    Issue Symptom Why would the keypad display Not Ready, but no zone number is displayed? Probable Cause An invisible zone is not ready. Possible Soultion Enter a valid pin number + off to display the zone number of the invisible zone that is not ready. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7447
    View full article
    ‎06-29-2018 05:41 PM
    What programmmer was used to program the wireless transmitters point transmission interval, point #, and house code on a D7112 wireless system?
    View full article
    ‎06-29-2018 05:35 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7430, DS7436, DS7432, DS7433, DS7460, DS7465, DS7460i, DS7465i
    View full article
    ‎06-29-2018 05:26 PM
    Issue How is the DS7432 eight input remote module interfaced with DS7400 series panels? Solution The DS7432 eight input remote module is interfaced with DS7400 series panels thru either the DS7430 (single mux bus) or DS7436 (dual mux bus) Multiplex Expansion Module. Connect the mux bus + terminal to the DS7432 module bus + and the respective mux bus - terminal to the DS7432 module bus - terminal. DS7432 is powered from Aux power from the DS7400(or X, Xi) panel terminals 7 (aux -) and 8 (aux +).  Connect power to DS7432 Power +, -. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, Ds7432, DS7430, DS7436
    View full article
    ‎06-29-2018 05:21 PM
    Issue Panel history shows a failure 3.   Solution   If panel is programmed to do a history dump to WDSRP but failed to communicate via the phone line that is programmed for remote callback, the panel will initiate a failure 3 trouble.   Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎06-29-2018 04:46 PM
    Issue Multiplex troubles and loss of communication to devices.   Solution   Perform the Following Troubleshooting steps 1. Check the voltage on the Mutilplex Bus 2. If the Voltage is 12VDC 3. Check and make sure the panel is out of programmer’s mode 4. Look for duplicate addresses 5. *Disable Bus lock 6. Make sure 12VDC is not connect to the Multiplex bus If the Voltage is 0 - . 3VDC 1. Check for Shorts on the multiplex loop 2. Check for reverse polarity to devices 3. If the device require diodes make sure the cathode side is on the positive side. * To Disable Bus Lock 1. Enter in to Programmers Mode  by code + #0 2. Type in 9999 *5 Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7430, DS7436
    View full article
    ‎06-29-2018 04:18 PM
    Issue This is a report that is generated when the system is armed and Closing Ring Back is enabled but the closing report is not. The Report 0 occurs because the panel does a phone check to see if dial-tone  is detected. If dial tone is not detected at the time the panel is armed it will display a Communication Fault on the Keypad it will generate this error in the History buffer. How are Report Fail 0 messages prevented? Solution To prevent these errors from occurring perform the following steps: On the DS7400/X version 1.xx 1. Enter in program mode by entering in the program PIN + #0 2. Depress 0011 03# 3. Hold the * key for 3 seconds to exit out of Program mode  On the DS7400Xi  Version 2.xx and Ver 3+ 1. Enter in program mode by entering in the program PIN + #0 2. Press 0000 03# 3. Hold the * key for 3 seconds to exit out of Program mode On the DS7400Xi Ver 4 1. Enter in program mode by entering in the program PIN + #0 2. Press 0000 03# 3. Hold the * key for 3 seconds to exit out of Program mode Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎06-29-2018 04:14 PM
    Issue Why does an invisible or silent zone activate the alarm output? Solution Probable Cause The output is programmed as "latch on alarm" (0) Possible Solution Program the output to follow zone alarms ( 6 ). Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎06-29-2018 04:07 PM
    Issue Symptom What would cause the programmer to display ( Plug in 7112) when you press send or receiver Diagnosis The programmer is not correctly connected to the D7112. Solution Verify that the data/power cord is plugged securely in the programmer port J4, on the D7112. Verify that the data/power cord is plugged securely into the communicator port on the D5200 programmer Check each conductor in the data/power cord for continuity Part numbers D7112, D5200
    View full article
    ‎06-29-2018 03:49 PM
    Issue 1.) The D7112 receives a busy signal for all ten attempts to reach the receiver. Diagnosis Calls are not reaching the receiver The receiver call load could be too great. Issue 2. )What would cause the receiver to answer the call and provide an acknowledgment tone, but the communicator does not transmit reports? Diagnosis The receiver is not producing the correct acknowledgement tones. The D136 relay in J10 for ground start phone systems is inserted incorrectly. Solution Verify that the correct prefixes and phone numbers for the receiver have been programmed into the D7112. Verify that the phone lines are not shorted between the phone company's equipment and the receiver by placing a call to the number for the receiver. If you hear the line ring, but the ring detector doesn't light, or if you hear a busy signal and the green "on the line" (OL) indicator is not lit, call the phone company for service. Verify that the receiver is producing a 2300 Hz or Modem II acknowledgment tone. Verify the D136 relay is in the socket J10 correctly.  
    View full article
    ‎06-28-2018 08:49 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    Top Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist