This website uses absolutely necessary cookies. If you consent to the use of convenience cookies, please click “Yes, I agree.” By clicking on “Privacy Settings.” you can change this setting at any time and withdraw your given consent. Icon down see more You can find detailled information in our Privacy Policy Icon forward-right
Icon up see less

Bosch Building Technologies

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 

    Security: Intrusion

    Sort by:
    ‎08-02-2018 08:34 PM
    Part numbers D9131A, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3, D9412GV3,
    View full article
    ‎08-02-2018 08:34 PM
    Overview: In order to comply with SIA CP-01 standards, GV2 revision 7.06 and higher panels have modified the method that points programmed for Swinger Bypass are bypassed. GV2 panel revisions 7.05 and earlier will automatically bypass points and report Swinger Bypass P### when these points erroneously report four trouble or alarm events within one hour of the first event. RPS revision 5.5 and higher provides a field called Swinger Bypass Count to be used in GV2 panels revision 7.06 and higher. This setting, between 1 and 4, selects the number of times that a point will automatically bypass after going into trouble or alarm, the selected number of times, within 1 hour of the first event. The Swinger Bypass Count setting is defaulted to 1 and if left unchanged Swinger Bypass points will Bypass after one alarm or trouble event. Further, new GV2 panels revision 7.06 and higher come with a default Swinger Bypass Count setting of 1. If programming with RPS revision 5.4 or earlier, the Swinger Bypass Count field will not be available to change and the setting will remain at 1. Likewise, if programming with the D5200 programmer using GV2Aux revision 1.01 or 1.00 the same problem will occur. RPS 5.5 or GV2Aux revision 1.02 or higher is required for programming. Issue Why do points bypass after one trouble or alarm event? Solution The point that generated 1 trouble or alarm and Bypassed uses a Point Index with Swinger Bypass set to Yes and the Swinger Bypass Count is set to 1. This setting is modified in GV2Aux>Misc>Swinger Bypass count in RPS rev 5.5 or higher. Using a D5200 programmer, GV2Aux revision 1.02 must be used. Swinger Count can be modified by entering group on Miscellaneous and then Swinger Count.
    View full article
    ‎08-02-2018 03:42 PM
    How to use the Auto Door function with access doors in G Series panels.
    View full article
    ‎08-02-2018 03:57 PM
    How to determine the current limit for devices powered from the DX1020 8 point expander.
    View full article
    ‎08-02-2018 04:01 PM
    There are 2 tests performed on the FA206i, Walk Test and Transmission Test. Walk Test: With cover in place, quickly (less than 1/2 second) pass a magnet near the Test Mode reed switch. This will activate a 1 minute walk test mode where the LED will light with each trip but no alarm signals will be transmitted. Transmission Test: With cover in place, hold a magnet near the Test Mode reed switch for at least one second. This will activate a one minute transmission test mode where the device will transmit alarm and restoral cycles at regular intervals for 1 minute. Note:  The FA206i LED only lights when in test mode.
    View full article
    ‎08-02-2018 04:11 PM
    How to clear the CHECK DIAL TONE message from the command center. D2012,D2212,D2412,D2812
    View full article
    ‎08-02-2018 08:33 PM
    Issue The instructions do not show how to interface the D169 to the D6412. Solution Voice Verification: Allows the panel to control a D169 2-way Voice Verification Module. The D169 allows the central station personnel to verify alarms with a two-way voice session with the premises. The premises phone line runs from the panel to the D169 and then to the premises phones. There are two other module connections to the panel: the programmable relay output (-12 VDC) programmed with the Voice Request output function (2,10), and a point (zone) programmed as a Voice Active point. The panel must also have one or more points with the Voice Verification option selected in the point index. When a point with Voice Verification generates an alarm event: The panel transmits the alarm report to the receiver at the central station. When the central station receiver acknowledges the report, the panel activates the Voice Request output function and starts a 30-second report delay time. All reports are delayed. The D169 has 30 seconds to start a two-way voice session. An operator at the central station picks up the phone line from the receiver with a DTMF telephone and presses [ 2 ]. At the premises, the D169 picked up the phone line when the panel activated the Voice Request output function. When it hears the DTMF tone from the operator pressing [ 2 ], it begins a two-way voice session by first shorting the panel’s Voice Active point. When the Voice Active point is shorted, the panel silences the non-fire alarm output (sets the Bell Timer to zero). Only the user can silence a fire alarm output. As long as the Voice Active point is shorted, the panel continues to keep reports buffered. The D169 ends the voice session by removing the short from the voice active point. The panel resets the bell time and Alarm Event Abort Window (assuming a user at the premises did not change the arming state of the panel during the voice session). Normal reporting (communication) resumes.                    Hardware Configuration 1.) J1 cable to the D6412 Brown to the negative out put Green to the Voice active zone one the panel Blue to the alarm out put if used White not used Red 12volts positive Black panel common 2.) J3 leave a default with A, and D jumped out. Need to follow instruction on the D169 for siren wiring, and operating instructions of the D169.                          
    View full article
    ‎08-02-2018 08:33 PM
    Issue How can the rising sun key or trapazoid key be used to activate an output on the D4412/D6412 control communicator?   Solution   Under Output Parameters, program a 1,15 for the trapazoid key or 2,0 for the rising sun key to activate an assigned output when the keyfob's alternate buttons are depressed.        
    View full article
    ‎08-02-2018 08:33 PM
    Overview: The Inovonics FA570 and FA575 High-Power Repeaters receive, decode and re-transmit signals from Inovonics FA-Series transmitters up to 4 miles in open field. Issue What is the difference between the FA570 and FA575? Solution The difference is the FA575 includes the ACC640 weatherproof enclosure to accommodate exterior applications as well as battery leads to hookup an external battery. Other then that, the units are exactly the same.
    View full article
    ‎08-02-2018 07:55 PM
    How to troubleshoot Unable to Arm the DS7400 using a valid passcode. DS7400,DS7400Xi,DS7400X,DS7400XIVER2,DS7400XIVER3+,DS7400XIVER4+.
    View full article
    ‎08-01-2018 10:47 PM
    Issue When does the D128 dual phone line switcher module indicate a phone line failure?   Solution   An amber phone line status LED lights on the D128 module when the control/communicator measures less than 25VDC or 10mA of current across the tip and ring of the telephone line. The D8112 and D9112 monitor the telephone lines for a programmable interval before indicating a trouble condition.
    View full article
    ‎08-01-2018 10:47 PM
    Issue What would cause the D6112 panel to send a zone 9, when arming the system? Solution D5200 Programing - 7.10 or 8.10 = Comb ID is set to yes in the program of the panel. With this prompt set to yes in the program, a zone 9 is sent when the panel is armed by the remote programmer, or command 1.
    View full article
    ‎08-01-2018 10:47 PM
    Overview: Charging circuit is overcharging the battery. Panel is damaged. Issue Reading 15vdc on the battery charging circuit.   Solution   Replace the panel. The voltage regulator is failing on the panel.
    View full article
    ‎08-01-2018 10:47 PM
    Overview: D4112 doesn’t arm or anything when code is entered at the keypad. Issue Nothing happens. Doesn’t arm or anything when code is entered at the keypad. Solution Connect programmer using coiled cord. Plug in plastic RJ phone type plug into COMMUNICATOR female connector on 5200 Plug brown connector on other end of coiled cord to programmer connection on 4112 Press ON button on 5200 Type in password at PASSWORD prompt, press enter. Top Line of 5200 shows PRODUCT HANDLERS Using the up/down arrows scroll down until 4112. Please blinking cursor on 4112 Press RED Enter Group button Place cursor on NEWRECORD Short the Standby pin on 4112 to ground momentarily Press RECV(COPY) button on programmer Receiving will be displayed at the top line of the 5200 Display Scroll down using arrow down key until cursor is on 2 PASSCODES Press ENTER GROUP button Passcode1 should have 234 in the field. To change field, press CLEAR key and type in the code to be used. Press enter The code is restricted to 4 characters but the user enters a prefix of 1, 2, 3, 4, 5…depending upon the slot. Example: PASSODE1 shows 234. The user code will be 1234   *** NOTE: Also make sure that the panel has a valid and functioning analog line.  The functionality of the system is dependent upond successful communications.
    View full article
    ‎08-01-2018 10:47 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3, D9412GV3, D7212GV4, D7412GV4, D9412GV4, B8512G, B9512G
    View full article
    ‎08-01-2018 07:53 PM
    How to force arm the D4112 or D6112 control panel.
    View full article
    ‎08-01-2018 10:46 PM
    Issue On 2000 series panel, point codes are programmed for points between 9 and 24. When programmed points are tested the keypad reads "PT(#) PT DISABLED (where # is the number of the point being tested). Solution Pt text (Point Text) was never changed from default that read "PT(#) PT DISABLED".
    View full article
    ‎08-01-2018 10:46 PM
    Issue How many zones can be programmed on the D8112G2?   Solution   The D8112G2 is capable to have 8 master zones that may be expanded to 134 individual zones of protection.
    View full article
    ‎08-01-2018 10:46 PM
    Issue   How many codes can be programmed for the D8112G2?   Solution   The D8112G2 can be programmed with up to 70 individual combinations.
    View full article
    ‎07-31-2018 10:42 PM
    How to configure the RK40 iCLASS pin reader for 26-bit output. ARD-RK40-09, ARD-RK40-14
    View full article
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist