If looking to apply power (complete the circuit):
NO of the DS150 to the Positive of the Maglock.
From the negative of the Maglock to the negative of the power supply.
From the Positive of the power supply to Common on the DS150.
If looking to remove power (break the circuit):
NC of the DS150 to the Positive of the Maglock.
From the negative of the Maglock to the negative of the power supply.
From the Positive of the power supply to Common on the DS150.
Note:
Generally we do fail safe not fail secure and the relay timer needs to be incremented.
If there is no G in the panel's name, there is no ground fault detection and the panel does not have an S4 pin.
If it has a single G in the name it has the chance it could be enabled if S4 is latched and under area 5 silent alarm relay there is a value other than 0.
If it’s a GV2, GV3 or GV4 and S4 is latched, ground fault detection is enabled.
If there is ground fault detection, latch S4 and measure DC voltage on Terminals 9 and 10: You should get 6.5-6.8 VDC Steady (not jumping around) when there isn't a ground fault.
If there is a ground fault it can take up to a minute to display and clear at the keypad.
Test Reports can be set up from Teraterm or RPS (requires firmware 2.0 or above). The test report timer (re)starts when the panel item is changed or when the module reboots, once the timer expires the test report is sent.
Step-by-step guide
Teraterm/RPS:
Go to System Configuration > Test Report Settings > Test Report Interval
The timer options are Off, 4hr, 6hr, 12hr, or 24h
Cause:
When the B420 or B426 has been programmed through the web interface and the setting; Panel Programming Enable has been set to NO, the B420 or B426 Ethernet Communicator module programming screen will look as displayed below with programming parameters not available for changing.
Solution:
The card will need to be accessed again through the web interface and Panel Programming Enable must be changed to read YES.
Log into the Web-Browser and select Maintenance. Click on the drop-down arrow beside the field; Panel Programming Enable and change it to Yes.
When programming the B420 or B426 to be connected to a GV3 or older panel the web interface is used.
When programming the B420 or B426 to be connected to a GV4 panel, use keypad programming.
Causes:
The heartbeat LED on the B426 is off.
No communication failure, trouble or communication module missing error messages at the keypad.
Solution
Check the TMPR pins next to the Ethernet port on the B426.
Remove the jumper from the pins; the B426s heartbeat LED will start flashing to show the firmware version on the board and then it will resume normal or trouble operation depending on the condition on the B426.
When the Tamper jumper is covering both pins the heartbeat LED is turned off to save power.
How to configure Door Control on both sides of a door with B8512G, B9512G or B6512 panels.
How to configure Door Control for Card-In and Card-Out with B8512G, B9512G or B6512 panels.
How to configure Access Control for Card-In / Card-Out with B8512G, B9512G or B6512 panels.
How to force Remote Programming Software (RPS) to connect to the panel from a keypad.
Remote Programming Software, Answer, 2000 series, D2212, D2412, D2812, D4412, D6412
How to correct Perimeter Instant Points going into Entry/Exit delay on the D4412 or D6412.
Why faulting a Perimeter Instant point may go into a delay countdown when the area is armed.