Issue
What voltage and current is the phone line monitor measuring to sense trouble on the phone line on the D7212B/D9112B panels?
Solution
The phone line monitor senses trouble when the voltage on the line falls below 4.5 to 7.5 VDC, or in the off-hook condition when the current is 8 to 13mA.
Issue
What type of RF receivers are compatible with the D4412/D6412?
Solution
The ITI receiver part number RF3226 and the Bosch receiver part number RF3224.
Issue
DS936 motion is causing an alarm when it is not seeing motion.
Solution
On the older version of this motion there will be a bank of DIP switches with four switches. Set the relay #4 to OFF for NC Alarm Relay Operation.
Overview: Power up charging status of the battey on a D4112 panel will send a trouble Zn 9 during Recharge cycle.
Issue
Why does the panel send a Trouble Zn 9 when the battery is charging?
Solution
After the AC is restored the battery will begin to charge. When the battery reaches a charging level of 11.1 volts, and maintains battery voltage level above 10.3 volts for 1 minute, the panel will RESET and a battery trouble (Trouble Zn 9) will be sent to the Central Station. When the battery reaches the charging level of 12.5 volts a Restoral Zn 9 is sent to the Central Station.
Issue
How is the battery test performed?
Solution
Type in (Command/ # ) 80 or a valid code # 80. If you want the sounder to trip with the battery test, type in #85.
If the Green power LED contiunes to flash after 10 seconds, the battery has failed and needs to be charged or replaced.
If the LED goes solid, the battery has passed.
How to correct the D8112/5505 not sending a Reboot report.
The 8112/5505 panel is communicating alarm and trouble signals but after resetting the panel it does not report the reboot.
5505,D8112A,D8112E1,D8112G1,D8112G2
Issue
Panel is not sending restorals when the point restores. Log also has no entries for restorals on the point.
Solution
This is normal if the panel is programmed not to send restorals.
In RAM/RPS check in the following: Point Index Codes > Point Indexes 1-16 or Point Indexes 17-31
Disable Restorals
Default: No Selections: Yes or No
Yes: Disable restoral reports for this point. No: Enable restoral reports for this point. When this option is enabled, a restoral report is sent to the receiver when the point returns to normal after being in an alarm or trouble condition.
If you are using the 5200:
In the 5200 check under:
9112B > Point Index > Point Index # (where # is a value between 1 and 31 only)
press the white ENTER key
press the down arrow key (red keys on the 5200)
Repeat until you are at P## Disable Restorals
Default: No Selection: Yes or No Yes = Disable Restoralreports for this point. No = Enable Restoralreports for this point. When this option is enabled, a Restoral report is sent to the receiver when the point returns to normal after being in an alarm or trouble condition. Use this item to automatically put this point back into the system.