    ‎06-15-2018 06:08 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎06-29-2018 03:49 PM
    Issue 1.) The D7112 receives a busy signal for all ten attempts to reach the receiver. Diagnosis Calls are not reaching the receiver The receiver call load could be too great. Issue 2. )What would cause the receiver to answer the call and provide an acknowledgment tone, but the communicator does not transmit reports? Diagnosis The receiver is not producing the correct acknowledgement tones. The D136 relay in J10 for ground start phone systems is inserted incorrectly. Solution Verify that the correct prefixes and phone numbers for the receiver have been programmed into the D7112. Verify that the phone lines are not shorted between the phone company's equipment and the receiver by placing a call to the number for the receiver. If you hear the line ring, but the ring detector doesn't light, or if you hear a busy signal and the green "on the line" (OL) indicator is not lit, call the phone company for service. Verify that the receiver is producing a 2300 Hz or Modem II acknowledgment tone. Verify the D136 relay is in the socket J10 correctly.  
    View full article
    ‎06-13-2018 02:33 PM
    How to to make the DS7220 or DS7240 panel local only.
    View full article
    ‎06-07-2018 05:13 PM
    How to make the D127 D127 Reversing Relay activate on alarm. The D127 does not activate when I trip the alarm.
    View full article
    ‎05-21-2018 08:16 PM
    What is the maximum number of users on a D8112A? D8112A
    View full article
    ‎06-14-2018 01:50 PM
    D279A,D279
    View full article
    ‎05-21-2018 05:48 PM
    Part numbers D5200, D2412
    View full article
    ‎06-15-2018 06:56 PM
    D4412 & D6412
    View full article
    ‎05-22-2018 04:00 PM
    Panel DS7400Xi
    View full article
    ‎05-22-2018 03:52 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7412G, D9124G, D9412G, D7412GV2, D9124GV2, D9412GV2, D7412GV3, D9412GV3, D7412GV4, D9412GV4,
    View full article
    ‎06-27-2018 05:37 PM
    Issue If using the D220A on the D2112 do I have the Exit Feature? Solution No, the D2112 does not have the Exit Feature. It uses the "Step Out Feature". The Exit Feature does appear on page 23 of the Users Guide, but that is because this Keypad can also be used on other 2000 Series Panels which have the Exit Feature.
    View full article
    ‎06-25-2018 03:50 PM
      Issue The D192G panel zone (point) is in trouble and the yellow LED is not on. Solution With the zone/point in trouble and No Yellow LED On there is a wiring fault. One of the following terminals do not have power connected to them. External Power In (EXT PWR IN) Auxiliary Power In (AUX PWR IN) Terminal 1 (AUX PWR IN) 13.75 VDC Terminal 2 (Common) Terminal 3 (Supervised Zone / Point) 2.50 VDC Normal Condiction < 1.50 VDC In Trouble Condiction Terminal 4 (Trigger) 13.75 VDC  In Alarm Only Terminal 5 (External Power In) 12 VDC or 24 VDC Depended on needed Output for the NAC's or Power Supply Terminal 6 (Common) This is the Common from an 24 VDC External Power Terminal 7 (Positive Alarm Output) Terminal 8 (Negative Alarm Output)
    View full article
    ‎06-17-2018 09:35 PM
    Issue User has authority in all areas but when presses Command 80, Command Center gives error tone and says Area 1 Ok for all on. Solution CMD 80 (All Areas On) and CMD 81 (All Areas Off) must be enabled in programming in order to function. 1)  Using Remote Programming: Go to Panel Wide Parameters; Global Open Close Options; Arming Options and find Enable Cmd 80 - All Areas All On, and Enable Cmd 81 - All Areas All Off and set both to Yes. 2)  Using Keypad Programming: Go to Nibble 1259 and enter 12 to enable both CMD 80 and CMD 81. Part numbers D4412, D6412, D625, D623
    View full article
    ‎05-22-2018 04:03 PM
    What is the correct part number of the printer module for the D9412 and D7412? D9131A,D9412G,D7412G,D7212G,D7412,D9412,D7212,D9412GV2,D7412GV2,D7212GV2,D9412GV3,D7412GV3,D7212GV3
    View full article
    ‎06-25-2018 06:37 PM
    Part numbers D2212, D2212B, D2212BE, D2412, D2412U, D2412UE, D2812, D2812U D2812P
    View full article
    ‎06-07-2018 03:28 PM
    How to restore Zone8 on the D7400 that won't clear even when strapped out with a 2.2K EOL.
    View full article
    ‎05-22-2018 04:13 PM
    Is it possible to turn on the system by just hitting the 9 key? D2012
    View full article
    ‎06-27-2018 07:06 PM
    Issue Unable to use Command 00 function. When CMD 00 is entered, keypad reads 'SYSTEM COMMAND' or 'INVALID KEYS'. Solution Un-Bypassing points on the D7112 panel must be done by using the FUNCTION Menu. Access the Function menu by pressing 'Enter' at the idle disarmed text. Press Next repeatedly until Function Menu displays. To access the UNBYPASS screen press enter on Function menu and Next until UNBYPASS displays. Display will read ENTER POINT NUMBER, enter the point number to be bypassed and press Enter. Display will read the text for the point, press enter again and screen will read POINT UNBYPASSED.
    View full article
    ‎06-15-2018 02:52 PM
    Issue D7112 Panel battery will not hold a charge. Solution A slow flashing (1 sec on, 1 sec off) yellow LED with the green CPU LED off indicates a power supply overload condition.  The panel detects the battery as missing and the power supply cannot meet the power demand of the devices on the panel. The panel is shut down.
    View full article
    ‎05-23-2018 08:24 PM
    How is AC fail time set in seconds instead of minutes? D7412,D7412G,D9412,D9412G
    View full article
    Top Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist