The Standby (Reset) pin is not locked down. The panel 12V backup battery is low or missing. Using the wrong product handler, for example, using 2112 instead of 2212. Too much Current Draw on panel. Disconnect devices from Aux Power and try again. Noise or interference on the keypad Data Bus. Disconnect all wires on the panel data terminals. Not enough free memory in the D5200 Programmer. There should be 60K free memory. Refer to KB article: How to Operate the D5200 Hand Held Programmer. The 2212 handler may be corrupted in the D5200. Delete the 2212 handler and re-download it. Refer to KB article: How to Operate the D5200 Hand Held Programmer. Low batteries in the D5200. Replace batteries using 4 C cells. Trying to program a panel that is not powered up The programming cord is not securely connected to the panel programming port or may be damaged. The DX4010V2 comes with a cord with a 4-pin Molex connector on one end and phone connector on other end. This cable may work as a substitute.
How is the answering machine bypass configured when trying to connect with RAM IV or RPS on a D2000 Series Panel? D2412,D2212,D2012,D2112,D2812,5600L,5600E
D5200 Programmer:
The D5200 needs to match a Data Lock code in the panel to access programming. Changing the panel Data Lock Code from the default of 12345 will prevent access.
Remote Programming Software:
RPS also needs to match the Data Lock code in the panel to access programming. Changing the panel Data Lock Code from the default of 12345 will prevent access.
RPS also needs to match the RPS Passcode (or RAM Passcode in legacy types) in order to allow access programming. Changing the default from 999999 will block RPS access.
Issue
On 2000 series panel, point codes are programmed for points between 9 and 24. When programmed points are tested the keypad reads "PT(#) PT DISABLED (where # is the number of the point being tested).
Solution
Pt text (Point Text) was never changed from default that read "PT(#) PT DISABLED".
Issue
What are the enviromental considerations for the proper operation of the Bosch control/communicators?
Solution
Indoor Dry.
Relative Humidity 5% to 85% noncondensing at +86 degrees Fahrenheit (+30 degrees Celsius).
Operating temperature would be +32 degrees Fahrenheit to +120 degrees Fahrenheit ( 0 degrees Celsius to 49 degrees Celsius ).
How to troubleshoot the 2000 series panel when the keypad reads Call For Service.
My D2212 reads "Call For Service" and does not show anything else. How do I determine the issue?
D2212, D2412, D2812
Issue
Does the D2112Command Centerbuzz discontinue after AC power is restored?
Solution
Yes. The Command Centertrouble buzz will timeout after 30 to 45 seconds following restoration of AC power.