How is the answering machine bypass configured when trying to connect with RAM IV or RPS on a D2000 Series Panel? D2412,D2212,D2012,D2112,D2812,5600L,5600E
Issue
Points are faulted but the panel does not react.
Solution
Points must be faulted for 500 milliseconds minimum.
*When using self resetting devices, some do not latch the contact in the faulted position but do show a fault trip via a latched LED.
Issue
What are the enviromental considerations for the proper operation of the Bosch control/communicators?
Solution
Indoor Dry.
Relative Humidity 5% to 85% noncondensing at +86 degrees Fahrenheit (+30 degrees Celsius).
Operating temperature would be +32 degrees Fahrenheit to +120 degrees Fahrenheit ( 0 degrees Celsius to 49 degrees Celsius ).
Issue
On 2000 series panel, point codes are programmed for points between 9 and 24. When programmed points are tested the keypad reads "PT(#) PT DISABLED (where # is the number of the point being tested).
Solution
Pt text (Point Text) was never changed from default that read "PT(#) PT DISABLED".
D5200 Programmer:
The D5200 needs to match a Data Lock code in the panel to access programming. Changing the panel Data Lock Code from the default of 12345 will prevent access.
Remote Programming Software:
RPS also needs to match the Data Lock code in the panel to access programming. Changing the panel Data Lock Code from the default of 12345 will prevent access.
RPS also needs to match the RPS Passcode (or RAM Passcode in legacy types) in order to allow access programming. Changing the default from 999999 will block RPS access.
Overview
New RF Receiver Trouble, Receiver ‘Jammed’
When used with RF Receivers with firmware 9.0 (or later), D2212Bs with revision 3.03 firmware (or later) can display two distinct trouble conditions. The receiver trouble display is expanded to two lines.
Issue
RCVR # TROUBLE 2111
# is the receiver number (7 or 8).
RCVR # TROUBLE 1211
# is the receiver number (7 or 8).
Solution
2111 in the second line indicates that no sensor has been heard from in a calculated interval. The interval depends on the number of sensors in the system.
1211 in the second line indicates that the receiver is in a ‘jammed’ condition. Interference is at a level that prevents sensor transmissions from being received.
Issue
Does the D2112Command Centerbuzz discontinue after AC power is restored?
Solution
Yes. The Command Centertrouble buzz will timeout after 30 to 45 seconds following restoration of AC power.