How to use the EN1210W or ISW-EN1210W with external contacts.
The EN1210W or ISW-EN1210W will not go normal when the external contacts are strapped out.
The door controlled by the door control module doesn't remain released when the REX sensor configured as 'resettable' continues to detect motion.
B901, D9210C, D9210B,DS150I,DS151I,DS160, DS161
How to interpret the 'Check Device' display on a D1255 or D1260 keypad.
Why does the keypad display "Check Device"?
How to locate which point generated the 'Check Device' display and modify programming to prevent the display.
Issue
What is the difference between the D133 an D134?
Solution
The D133 has a single relay rated at 2A @ 30 VDC – 0.6A @ 125 VAC.
The D134 has two relays rated at 2A @ 30 VDC – 0.6A @ 125 VAC.
Current draw for the Relay is 40 mA per relay when activated.
Issue
Can I mix Heat Detectors and 2 wire smokes with a sounder when using a D132A Smoke Detector Polarity Reversing Module?
Solution
No. When a Heat detector goes into alarm it puts a short on the input zone to indicate the alarm. The D132A uses Aux power from the panel when the polarity reversal takes place and since a heat detector does not reset when polarity is reversed, it would put a direct short on the Aux power of the panel. Consequently everything connected to the same Aux power terminals would not function.