Bosch Building Technologies

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 

    Security: Intrusion

    Sort by:
    ‎07-26-2018 05:07 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3, D9412GV3, 
    View full article
    ‎07-26-2018 05:07 PM
           
    View full article
    ‎07-26-2018 05:07 PM
    Issue What is the part number for the back up battery for the DS415i and the DS445? Solution The P333 Backup Battery is designed for use with both the DS445 and DS415i Photoelectric Beam Detectors. When using the P333 with the DS415i, the polarity plug in the battery connector must be removed. Pull the white plug out of the connector using a pair of needle nosed pliers before connecting it to the DS415i. When the P333 battery is used with the DS445, there are no modifications necessary.   Part numbers P333, DS445, DS415i  
    View full article
    ‎07-26-2018 05:06 PM
    Part numbers D2212, D2212B, D2212BE, D2412, D2412U, D2412UE, D2812, D2812U, D2812P, D222A, D223A, D202A, D220A
    View full article
    ‎07-26-2018 05:06 PM
    Part numbers D7412,D9124, D9412, D7212G, D7412G, D9124G, D9412G, D7412GV2, D7412GV2, D9124GV2, D9412GV2,D7412GV3, D9412GV3,
    View full article
    ‎07-26-2018 05:03 PM
    What are the maximum number of 2 wire smokes that can be applied to loop B?
    View full article
    ‎07-26-2018 05:02 PM
    D462 Pull Stations - Do we make a plastic cover or tamper proof cover?
    View full article
    ‎07-26-2018 05:02 PM
    What is the expansion module for the DS7080IP32 panel?
    View full article
    ‎07-26-2018 03:27 PM
    Issue The panel does not report any alarms or cancel reports when a non-fire point goes into an alarm and then is silenced by the code at the keypad.   Solution   Alarm Event Abort (Non-Fire Points Only): assigns the abort feature to a Point Index. See Alarm Event Abort Window to learn how to set the Alarm Event Abort Window. If a user acknowledges a non-fire alarm point event by entering their passcode before the Alarm Event Abort Window expires: The alarm event is aborted. Alarm, Cancel* and Restoral reports associated with the alarm are not transmitted and the event becomes a local only event. *A Cancel window starts with the initiation of the alarm event and follows the Bell Time. If the user acknowledges the alarm inside the Cancel window (bell time), a Cancel or a Fire Cancel report is sent. If the Abort feature is enabled, the Cancel report is sent if the user acknowledges the alarm after the Abort window has expired, but before the bell time expires. SIA: The Cancel Window is required for SIA Control Panel Standard for False Alarm Reduction. The user hears a unique three long beep tone at the command center. The text command centers indicate that the alarm was aborted on the display. It appears as a slow flash in Alarm Memory at LED command centers. IMPORTANT: This option has no effect on Fire and Fire with Verification point types. The Alarm Event Abort feature does not apply to alarm events initiated by the ABC Keys, the Duress passcode or the keyfob Panic function. SIA: Alarm Event Abort is required for the SIA Control Panel Standard for False Alarm Reduction.  Alarm Event Abort Window-Nibble 1034 Default: 30 seconds Selections: 15 seconds, 30 seconds, 45 seconds Parameter Description This parameter sets the length of the Alarm Event Abort window. See Point Index Options 1 to apply the Alarm Event Abort feature to a point index. IMPORTANT: This option only affects non-fire points. Fire and Fire with Alarm Verification points are not affected by enabling this option. If a user acknowledges a non-fire alarm event by entering his/her passcode before the Alarm Event Abort window expires: The alarm event is aborted. Alarm, Cancel* and Restoral reports associated with the alarm are not transmitted. The alarm event becomes a local only event. The user hears a unique three long beep tone at the Command Center. The Text Command Center indicates the aborted alarm on the display. The LED Command Centers indicate the aborted alarm with a slow flash in Alarm Memory. * A Cancel window starts with the initiation of the alarm event and follows Bell Time. If the user acknowledges the alarm inside the Cancel window (Bell Time), a Cancel or Fire Cancel report is sent. If the Abort feature is enabled, the Cancel report is sent if the user acknowledges the alarm after the Abort window has expired but before Bell Time expires. SIA: Alarm Event Abort Window is required for SIA Control Panel Standard for False Alarm Reduction.
    View full article
    ‎07-26-2018 03:26 PM
    What are the steps on programming  the panel to send AC Fail and AC Restoral reports?
    View full article
    ‎07-26-2018 03:26 PM
    What is the setup on programming panel's "AC fail" timer?
    View full article
    ‎07-26-2018 03:26 PM
    Does the buzzer sound if the door is open past the shunt time even if no buzz time is programmed in RADXAXS under STRIKE PROFILES
    View full article
    ‎07-26-2018 03:25 PM
    Issue How far can the D9131A be installed remoted from the control panel?   Solution   The D9131A can be installed a maximum of 1000 ft. (305m) from the panel using 22 AWG solid copper wire.            
    View full article
    ‎07-25-2018 10:18 PM
    How to determine which GV4 panel types can be upgraded from ver 1.x to ver 2.x.
    View full article
    ‎07-25-2018 10:08 PM
    How to determine compatibility with iPhone or Android application using a Cellular Network. What is required of the GV4 series panel in order to use the iPhone or Android application over a cellular network? B450, B440, B441, B442, B443
    View full article
    ‎07-25-2018 09:46 PM
    Issue If the Central Station receives a signal in 4 x 2 format from a D2112 panel, how can that signal be deciphered using the programmed settings in the panel ? Solution The report code will consist of data digit 1 and data digit 2. When sending signals in Pulse, the first digit of the reported signal must be set to a particular report group in panel programming. The second digit will contain the point number or user number or event number that relates to digit one. The chart below shows the Description of what the second digit of a reported code would be if the first digit were programmed as show below. NOTE: The first digit could be any selection 0-9 or B-F for any of the report groups. To decipher the reported code: If using the D5200, look in programming under Receiver Format and RPT Groups for Pulse. The number entered beside the Report Group is what will come in as the first reported digit. Using the chart below, the point number or user number or event number that pertains to the second digit is described.                 In remote programming, view the report section of the program to determine the report group programmed for Digit one. Using the chart below, the point number or user number or event number that pertains to the second digit is described.  
    View full article
    ‎07-25-2018 09:28 PM
    Part numbers D2212, D2212B, D2212BE, D2412, D2412U, D2412UE, D2812, D2812U, D2812P
    View full article
    100% helpful (1/1)
    ‎07-25-2018 09:45 PM
    Part numbers D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G
    View full article
    ‎07-25-2018 08:11 PM
    Part numbers D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G
    View full article
    ‎07-25-2018 07:29 PM
    Part numbers D2212B, D2212BE, D2412, D2412U, D2412UE, D2812, D2812U, D2812P, D222A, D223A
    View full article
    Top Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist