Issue
When programming the D279 keypad point index on the 7000/9000, G, GV2, & GV3 series panels, how should the type and response be programmed?
Solution
Program a type 7 for D279 (O/C Non-Priority): The D279 provides point arming and disarming independent of the area arm state. A non-priority D279 point arm state does not affect the area arm state. Point Response must be programmed 1. Program type 8 for D279 (O/C Priority): The D279 provides point arming and disarming independent of the area arm state. A priority D279 point must be armed before an area can be armed. Program Point Response as 2.
Issue
What 2 wire smoke detectors have been UL listed compatible with the D4112?
Solution
Note : The D4112 is not UL listed for Commercial Fire Applications. This control does not support multiple detectors in alarm. Do not use smoke detectors from different manufacturers on the same circuit.
Radionics
Head D262 / Base D260 (20 per loop)
Detection Systems
Head DS200 / Base MB200-2W (10 per loop)
Head DS200HD / Base MB200-2W (10 per loop)
System Sensor
Head 1400 / Base N/A (10 per loop)
Head 2400 / Base N/A (10 per loop)
Head 2400th / Base N/A (10 per loop)
Head 1451 / Base B401, B401B (10 per loop)
Head 1451DH / Base DH400 (10 per loop)
Head 2451 / Base B401, B401B, DH400 (10 per loop)
Head 2451TH / Base B401, B401B, DH400 (10 per loop)
Head 2300T / Base N/A (10 per loop)
Issue
What is the part number for the back up battery for the DS415i and the DS445?
Solution
The P333 Backup Battery is designed for use with both the DS445 and DS415i Photoelectric Beam Detectors. When using the P333 with the DS415i, the polarity plug in the battery connector must be removed. Pull the white plug out of the connector using a pair of needle nosed pliers before connecting it to the DS415i. When the P333 battery is used with the DS445, there are no modifications necessary.
Part numbers P333, DS445, DS415i
Issue
The panel does not report any alarms or cancel reports when a non-fire point goes into an alarm and then is silenced by the code at the keypad.
Solution
Alarm Event Abort (Non-Fire Points Only): assigns the abort feature to a Point Index. See Alarm Event Abort Window to learn how to set the Alarm Event Abort Window. If a user acknowledges a non-fire alarm point event by entering their passcode before the Alarm Event Abort Window expires:
The alarm event is aborted. Alarm, Cancel* and Restoral reports associated with the alarm are not transmitted and the event becomes a local only event.
*A Cancel window starts with the initiation of the alarm event and follows the Bell Time. If the user acknowledges the alarm inside the Cancel window (bell time), a Cancel or a Fire Cancel report is sent. If the Abort feature is enabled, the Cancel report is sent if the user acknowledges the alarm after the Abort window has expired, but before the bell time expires.
SIA: The Cancel Window is required for SIA Control Panel Standard for False Alarm Reduction.
The user hears a unique three long beep tone at the command center.
The text command centers indicate that the alarm was aborted on the display. It appears as a slow flash in Alarm Memory at LED command centers.
IMPORTANT: This option has no effect on Fire and Fire with Verification point types. The Alarm Event Abort feature does not apply to alarm events initiated by the ABC Keys, the Duress passcode or the keyfob Panic function.
SIA: Alarm Event Abort is required for the SIA Control Panel Standard for False Alarm Reduction.
Alarm Event Abort Window-Nibble 1034 Default: 30 seconds Selections: 15 seconds, 30 seconds, 45 seconds
Parameter Description This parameter sets the length of the Alarm Event Abort window. See Point Index Options 1 to apply the Alarm Event Abort feature to a point index.
IMPORTANT: This option only affects non-fire points. Fire and Fire with Alarm Verification points are not affected by enabling this option.
If a user acknowledges a non-fire alarm event by entering his/her passcode before the Alarm Event Abort window expires:
The alarm event is aborted. Alarm, Cancel* and Restoral reports associated with the alarm are not transmitted. The alarm event becomes a local only event.
The user hears a unique three long beep tone at the Command Center.
The Text Command Center indicates the aborted alarm on the display. The LED Command Centers indicate the aborted alarm with a slow flash in Alarm Memory.
* A Cancel window starts with the initiation of the alarm event and follows Bell Time. If the user acknowledges the alarm inside the Cancel window (Bell Time), a Cancel or Fire Cancel report is sent. If the Abort feature is enabled, the Cancel report is sent if the user acknowledges the alarm after the Abort window has expired but before Bell Time expires.
SIA: Alarm Event Abort Window is required for SIA Control Panel Standard for False Alarm Reduction.
Issue
How far can the D9131A be installed remoted from the control panel?
Solution
The D9131A can be installed a maximum of 1000 ft. (305m) from the panel using 22 AWG solid copper wire.