How to use the EN1210W or ISW-EN1210W with external contacts.
The EN1210W or ISW-EN1210W will not go normal when the external contacts are strapped out.
Issue
How many 2 wire smokes will the D7112 support on zone 1?
Solution
Manufacturer & Models, and the number of smokes
Radionics D262 with the D260 base = 20 smokes
DS200 with the MB200-2w base = 10 smokes
System Sensor 1400 = 10 smokes
System Sensor 2400 = 10 smokes
System Sensor 2400TH = 10 smokes
System Sensor 1451 with the B401 base = 10 smokes
System Sensor 1451 DH with the DH400 base = 10 smokes
System Sensor 2451 with the B401,B401B or DH400 = 10 smokes
System Sensor 2451TH with the B401,B401B or DH400 = 10 smokes
System Sensor 2300T = 10 smokes
How to correct point and user numbers reporting in a non-standard format, example; points 1-9 reporting as 101-109 or users 006-013 reporting as 601-608.
Cause:
When the B420 or B426 has been programmed through the web interface and the setting; Panel Programming Enable has been set to NO, the B420 or B426 Ethernet Communicator module programming screen will look as displayed below with programming parameters not available for changing.
Solution:
The card will need to be accessed again through the web interface and Panel Programming Enable must be changed to read YES.
Log into the Web-Browser and select Maintenance. Click on the drop-down arrow beside the field; Panel Programming Enable and change it to Yes.
When programming the B420 or B426 to be connected to a GV3 or older panel the web interface is used.
When programming the B420 or B426 to be connected to a GV4 panel, use keypad programming.