How to force Remote Programming Software (RPS) to connect to the panel from a keypad.
Remote Programming Software, Answer, 2000 series, D2212, D2412, D2812, D4412, D6412
Issue
What is the Part # for the ribbon cable that is used with the D128 or D928?
Solution
Call Spare Parts (800) 894-5215 - Ribbon Cable Part Number is 15-03131-000-B.
Issue
What is RPS Call Back?
Solution
RPS Call Back
Default setting is No.
Selections are Yes or No
Parameter Description
Using this function allows the control panel, after it has verified the RPS passcode, to provide an additional level of security by hanging up and dialing the RPS phone number to call RPS at the central station prior to allowing any upload or download.
Important: When using the RPS Callback function, enter a "C" as the last digit in the RPS phone number if DTMF dialing is used.
Parameter Options
Yes: When the control panel hears the proper RPS passcode, it hangs up the phone, seizes the phone line, then dials the programmed RPS phone number (see RPS Ph ). This ensures that only the control panel communicates with the RPS PC connected to the dialed phone number.
No: The RPS session is initiated immediately; no call back is required. The control panel engages in RPS sessions when called from any phone number and a proper RPS passcode is identified.
How to configure two readers to a single door, one to enter through a door and a second to exit through the door. Access Control, Reader, Door, Enter, Exit, Card, Egress, D9210B, D9210C, D7412, D9412, D7412G, D9412G, D7412GV2, D9412GV2, D7412GV3, D9412GV3, D7412GV4, D9412GV4
Once a custom function is created, how does it run at the keypad? D9412G,D7412G,D7212,D7212B,D7212B1,D7212G,D9112,D9112B,D9112B1,D7412,D9412,D7212GV2,D7212GV3,D7212GV4,D7412GV2,D7412GV3,D7412GV4,D9412GV2,D9412GV3,D9412GV
Issue
Trouble tones will clear and then return one hour later.
Solution
RF Sensor Low Battery
With earlier revisions of panel firmware, users could silence a low RF fire sensor battery trouble indefinitely. With revision 3.03 (or later), the panel restarts the trouble sounder at the keypad within four hours if the low battery in the fire sensor is not replaced.