Issue
How can I setup Open/Close on a 2000 series panel?
Solution
Using RPS/RAMIV
1. Connect to the control via modem/RPS and receive all panel data and save to your RPS database.
2. Go to the Reports section of the program.
A. Turn on All-On reports by selecting Yes.
B. Turn on Part-On reports by selecting Yes.
3. Save your changes and send the changed data back to the control. Test it out.
Using 5200
1. Latch the installer clip on the control panel and receive a fresh copy of the panel data.
2. After you see Receive Successful on your 5200, go to the Reports section of the program.
3. Using the white SPACE bar on the 5200 press it to toggle NO to YES to turn on O/C for both ALL ON and PART ON.
4. Press the red SEND LOAD key, disconnect the programmer and unclip the installer switch. Test it out.
How to troubleshoot the 2000 series panel when the keypad reads Call For Service.
My D2212 reads "Call For Service" and does not show anything else. How do I determine the issue?
D2212, D2412, D2812
How to initiate a programmed test time on 2000 Series control panels.
Does the D2212 Timer Test Need to be Initiated from the Keypad?
D2812,D220A (8 led),D2412,D2212,D222A LCD,D223A LCD,D220A,D222,D223
Overview
New RF Receiver Trouble, Receiver ‘Jammed’
When used with RF Receivers with firmware 9.0 (or later), D2212Bs with revision 3.03 firmware (or later) can display two distinct trouble conditions. The receiver trouble display is expanded to two lines.
Issue
RCVR # TROUBLE 2111
# is the receiver number (7 or 8).
RCVR # TROUBLE 1211
# is the receiver number (7 or 8).
Solution
2111 in the second line indicates that no sensor has been heard from in a calculated interval. The interval depends on the number of sensors in the system.
1211 in the second line indicates that the receiver is in a ‘jammed’ condition. Interference is at a level that prevents sensor transmissions from being received.
Issue
Trouble tones will clear and then return one hour later.
Solution
RF Sensor Low Battery
With earlier revisions of panel firmware, users could silence a low RF fire sensor battery trouble indefinitely. With revision 3.03 (or later), the panel restarts the trouble sounder at the keypad within four hours if the low battery in the fire sensor is not replaced.
Overview
Remote Program (Key 2)
After pressing the [2] key and entering an Owner passcode to enter the Remote Program Mode, the display shows SYSTEM PROGRAM IN PROGRESS. If the [CLEAR] key is pressed to return to the OFF state, the system will not allow re-entering the Remote Program Mode for 30 seconds.
Issue
Remote Program (Key 2) and owners code will not work twice in a row.
Solution
D2212B Firmware Revision 3.03
After pressing the [2] key and entering an Owner passcode to enter the Remote Program Mode, the display shows SYSTEM PROGRAM IN PROGRESS.
If the [CLEAR] key is pressed to return to the OFF state, the system will not allow re-entering the Remote Program Mode for 30 seconds.