Bosch Building Technologies

    cancel
    Showing results for 
    Search instead for 
    Did you mean: 

    Security: Intrusion

    Sort by:
    ‎07-02-2018 09:37 PM
    How is the  sensitivity changed on the DS935Z detector? DS935Z
    View full article
    ‎07-02-2018 09:20 PM
    Issue What readers are compatable with the D9210B Interface Module?   Solution   Refer to the Data Sheet below.
    View full article
    ‎07-02-2018 09:03 PM
    Issue Bell output only activates for 30 seconds even though it is programmed for 99 minutes. Solution When the fire bell time (address 0195 in version 3, address 4032 in version 4) or burglary bell time (address 0196 in version 3, address 4033 in version 4) is set to 99 for a DS7400Xi version 3 or 4 this sets the bell cutoff time to 30 seconds. For indefinite bell output then these programming addresses should be set to 00.  For 98 minutes of bell output these should be set to 98. Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎07-02-2018 08:59 PM
    Overview: Bosch Security Systems D113 Battery Lead Supervision Module provides supervision of the battery lead connection between the module and one or two batteries in a 12 VDC system. The D113 meets NFPA 72 requirements for Battery Lead Supervision for Fire Alarm Panels. Issue When is a D113 module needed?   Solution   When a fire panel is using more than 1 backup battery for back up power and or when using more than 1 battery and battery supervision is required or wanted for the system. Note: August 2001 Release Notes Affects: D113 Installation Manual (P/N: 74-07468-000-B) Avoid Short Circuits - Short circuits on the charger wiring between the D113 and the control panel will damage the D113 module. To prevent damage to the module or panel, and possible personal injury, avoid shorting any control panel battery wiring. Battery Fault Signaling - There are two ways that the D113 signals a fault condition: with the supervisory output connected to the zone input of a panel and through the charger wires from the panel. As long as the D113 module is properly receiving power to operate, it will indicate faults using the supervisory output. If the D113 loses power (for example, batteries are connected backwards), the supervisory output may restore and be replaced by a battery fault that is detected through the charger leads. A restoral on the zone input, which is replaced by a control panel battery fault, indicates total failure of the battery  system.         Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G  
    View full article
    ‎07-02-2018 05:01 PM
    Issue Keypad says "loopback bad" and scrolls thru all the characters.   Solution   Keypad not addressed correctly. Switch dipswitch dip# 1 off   Part numbers D8112A, D1252, D1252A
    View full article
    ‎07-02-2018 04:27 PM
    Issue What would cause the LED to flash? Solution Here is a list of possible reasons for the DS774Z Red LED to flash. Flashing 2 times is a Motion Monitor Timeout Flashing 3 times  Antimask Detection Flashing 4 times  PIR Self test failure Flashing 5  times Low Input Power or Relay Failure          
    View full article
    ‎07-02-2018 04:17 PM
    Issue Can not get some of the functions to work on the command center. Overveiw: Some functions require you to enter single partition mode when using a master keypad. Soultion The following command require that you are in single partition mode when entering from a master keypad. ( valid code ## ) History read-back Chime mode Checking zone status Checking zone troubles status Bypassing zones      Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7447, DS745, DS7447E,  
    View full article
    ‎07-02-2018 04:07 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+,
    View full article
    ‎07-02-2018 04:02 PM
    Overview: Setting program entry 104 OnBat toYes, enables the alpha display "On Batry" and turns on buzzer when battery is draining faster that it is charging, i.e.: power load on D8112 is more than AC can supply alone.  If this item is programmed YES, the Alpha Command Center will buzz during test reports.   Issue   Every time the D8112 sends a test report, the keypad buzzes until CMD 4 is entered. Solution If program item 104 OnBat (found under Special Alpha Cmd in D8112 Main handler) is set to YES, the Alpha Command Center will buzz during test reports. Part numbers D8112, D8112A, D8112E, D8112E1, D8112G, D8112G1, D8112G2, D1252, D1252A, D360
    View full article
    ‎07-02-2018 03:56 PM
    Issue The DS160/161 fails to operate after multiple trips or cycles. Solution Cause: Possible wrong part (Op- Amp) There are some problems withLot #'s 578C, 579C, 580C with the DS160/161. The DS160/161 could stop detecting after multiple activation, and will not work. Send the customer an advance replacement. Anything passed Lot 580C should have the fix Not all DS160/161 are a problem.
    View full article
    ‎07-02-2018 03:19 PM
    Part numbers DS7400X, DS7400, DS7400Xi, DS7400XIVER2, DS7400XIVER3+, DS7400XIVER4+, DS7447, DS7447E
    View full article
    ‎07-02-2018 03:12 PM
    Issue The D4412/D6412 panel reports zones (zones  10o,101,102)when reporting to a D6500 receiver sending Modem IIIa2.   Solution   Only the following central station receivers support the D6412/D4412 Modem IIIa2 Format: • D6600 with CPU v.01.01.03 (or higher) • D6500 with D6511 MPU v1.05 (or higher) .The D6500 with D6510 MPU does not support the D6412/D4412 Modem IIIa2 Format. Note: Normal operation when using the A,B,C keys, reporting is as follows: [A] key reports as Zone 100 for all areas [B] key reports as Zone 101 for all areas [C] key reports as Zone 102 for all areas
    View full article
    ‎07-02-2018 02:58 PM
    Issue How to reset Smoke Detectors after an alarm. Overview: A D136 Plug in Relay is required see below. Solution Reset Detectors By using COMMAND 47, you are able to reset faulted detection devices such as smoke detectors, shock sensors or other power resettable devices from your Alpha II Command Center(Note: Ask your alarm technician which detection zones you may reset from the Alpha II by entering COMMAND 47). NOTE: If you enter COMMAND 47 and the detector resets momentarily, but then returns to a faulted condition, the detector may be faulty or still in an alarm mode. Contact your alarm company and describe the problem in detail. To use COMMAND 47: 1. Ensure security system is disarmed. 2. Press the COMMAND bar. The display should show "SYSTEM COMMAND". 3. Press and release the 4 key. Now press and release the 7 key. The display shows RESET SENSORS for approximately 10 seconds.   Part numbers D8112, D8112A, D8112E, D8112E1, D8112G, D8112G1, D8112G2  
    View full article
    ‎07-02-2018 02:48 PM
    Issue How can the calendar be adjusted on the D8112? Solution Perform the following steps: Your security system has an internal calendar which it uses to schedule automatic test reports and other functions. This calendar can be programmed to run a weekly or monthly time schedule. If programmed for a weekly schedule, the display shows the day of the week followed by the number of the day (for example, MON 2). If programmed for a monthly schedule, the display shows the month, followed by the day of the month (for example, MAR 20). To use COMMAND 46: 1. Ensure that the security system is disarmed. 2. Press the COMMAND bar. The display should show SYSTEM COMMAND. 3. Press and release the 4 key, then press and release the6 key. The display should show SET DATE=(date disply). To set a new date display, simply enter the desired date with the number keys on the Alpha II keypad. See the directions on right for month mode or day of the week mode display adjustments.< /FONT> 4. When the display is correct, press the COMMAND bar to exit from this mode. If the COMMAND bar is not pressed, the new date will not be entered and the Alpha II will revert back to the original date displayed. If no keys are pressed for 20 seconds, the Alpha II automatically exits from this mode. Day of Month Schedule: EXAMPLE: To set a date of May 17, you would enter the following: Press the 0 + 5 keys ("05" is the code for May, the fifth month of the year), then press the 1 + 7 keys. The display shows SET DATE= MAY 17. Numerical entries to set month display 01 JAN 04 APR 07 JUL 10 OCT 02 FEB 05 MAY 08 AUG 11 NOV 03 MAR 06 JUN 09 SEP 12 DEC Day of Week Schedule: EXAMPLE: To set the day of week display for Friday, you would enter the following. Press the 6 key. The display shows SET DATE= FRI 6. Numerical Entries to Set Day of Week Display 1 SUN 3 TUE 5 THU 7 SAT 2 MON 4 WED 6 FRI Part numbers D8112, D8112A, D8112E, D8112E1, D8112G, D8112G1, D8112G2, D1252, D1252A
    View full article
    ‎07-02-2018 02:44 PM
    Issue How can the D8112 clock be set? Solution COMMAND 45 is used to adjust the time display on your Alpha II Command Center. When you enter COMMAND 4 the Alpha clock is shown in the display momentarily. By entering COMMAND 45, the clock is displayed and may be adjusted with the Alpha II keypad. IMPORTANT: The time should be checked and adjusted at least once a month to insure accuracy. 24-Hour clock settings 1:00pm = 13:00 5:00pm = 17:00 9:00pm = 21:00 2:00pm = 14:00 6:00pm = 18:00 10:00pm = 22:00 3:00pm = 15:00 7:00pm = 19:00 11:00pm = 23:00 4:00pm = 16:00 8:00pm = 20:00 12:01am = 00:01 To use COMMAND 45: 1. Ensure that the security system is disarmed. 2. Press the COMMAND bar. The display should show SYSTEM COMMAND, press 4, 5. 3. Press and release the 4 key, then press and release the 5 key. The display should show SET TIME=(time disply). To set a new time display, simply enter the desired time with the number keys on the Alpha II keypad. (Remember, the clock is set in military time standards, also known as the 24-hour clock. Enter four digits for a complete time setting.) The new time scrolls into the display from right to left, replacing the old display. For example, to set a time of 1:15 a.m. you would enter the following: Press the 0 + 1 + 1 + 5 keys. The display shows SET TIME= 01:15. 4. When the display is correct, press the COMMAND bar to enter the time and exit from this mode. If the COMMAND bar is not pressed, the new time will not be entered and the Alpha II will revert back to the original time displayed. If no keys are pressed for 20 seconds, the Alpha II automatically exits from this mode. Part numbers D8112, D8112A, D8112E, D8112E1, D8112G, D8112G1, D8112G2, D1252, D1252A
    View full article
    ‎06-29-2018 10:46 PM
    How to determine the max Number of B208 Limit the number of B308's that can be used.  Does Max Number of B208 Limit the number of B308's that can be used?
    View full article
    ‎06-29-2018 10:01 PM
    How to determine how many network interfaces can be added to the control panel. B420 B426 DX4020
    View full article
    ‎06-29-2018 08:33 PM
    How to correct the RS Control APP message:  "System is Disabled".
    View full article
    ‎06-29-2018 08:31 PM
    How to set the test report time on the 190 Test Report Timer module for the 4012/8012 panel. D4012,D8012
    View full article
    ‎06-29-2018 07:41 PM
    Part numbers D7212B, D9112B, D7212B1, D9112B1, D7212, D7412, D9112, D9124, D9412, D7212G, D7412G, D7412G, D9124G, D9412G, D7212GV2, D7412GV2, D7412GV2, D9124GV2, D9412GV2, D7212GV3, D7412GV3,D7412GV3, D9412GV3, D7212GV4, D7412GV4, D7412GV4, D9412GV4, B8512G, B9512G
    View full article
    Top Contributors
    Icon--AD-black-48x48Icon--address-consumer-data-black-48x48Icon--appointment-black-48x48Icon--back-left-black-48x48Icon--calendar-black-48x48Icon--center-alignedIcon--Checkbox-checkIcon--clock-black-48x48Icon--close-black-48x48Icon--compare-black-48x48Icon--confirmation-black-48x48Icon--dealer-details-black-48x48Icon--delete-black-48x48Icon--delivery-black-48x48Icon--down-black-48x48Icon--download-black-48x48Ic-OverlayAlertIcon--externallink-black-48x48Icon-Filledforward-right_adjustedIcon--grid-view-black-48x48IC_gd_Check-Circle170821_Icons_Community170823_Bosch_Icons170823_Bosch_Icons170821_Icons_CommunityIC-logout170821_Icons_Community170825_Bosch_Icons170821_Icons_CommunityIC-shopping-cart2170821_Icons_CommunityIC-upIC_UserIcon--imageIcon--info-i-black-48x48Icon--left-alignedIcon--Less-minimize-black-48x48Icon-FilledIcon--List-Check-grennIcon--List-Check-blackIcon--List-Cross-blackIcon--list-view-mobile-black-48x48Icon--list-view-black-48x48Icon--More-Maximize-black-48x48Icon--my-product-black-48x48Icon--newsletter-black-48x48Icon--payment-black-48x48Icon--print-black-48x48Icon--promotion-black-48x48Icon--registration-black-48x48Icon--Reset-black-48x48Icon--right-alignedshare-circle1Icon--share-black-48x48Icon--shopping-bag-black-48x48Icon-shopping-cartIcon--start-play-black-48x48Icon--store-locator-black-48x48Ic-OverlayAlertIcon--summary-black-48x48tumblrIcon-FilledvineIc-OverlayAlertwhishlist