How to control the D8112 buzz when test reports are sent.
The D8112 panel buzzes when it sends test reports, how can I stop the buzz?
D8112G2,D8112E1,D8112G1,D8112A
1. Ensure the area is disarmed.
2. Press Cmd + 4 + 2. The flashing Cmd light is a prompt to enter a valid passcode.
3. Enter a valid passcode and the D621 displays system trouble events by lighting the point indicators (zone leds)as described below:
Zone 1 Lit steady = Telephone line Fail
Zone 1 Slow Flash = Comm Fail, Destination 1
Zone 1 Fast Flash = Comm Fail, Destination 2
Zone 2 Lit steady = Alternate Comm Trouble
Zone 3 Lit steady = Installer Switch Closed
Zone 4 Lit steady = Backup Battery low
Zone 4 Lit steady = Slow Flash = Backup Battery Missing
Zone 5 Lit steady = Bell Supervision Fail
Zone 6 Lit steady = RF Receiver Jamming
Zone 6 Slow Flash = RF Receiver Trouble
Zone 7 Lit steady = Data Bus Device Missing
Zone 7 Slow Flash = Data Bus Device Tamper
Zone 7 Fast Flash = Data Buss Device Trouble/Reset
Zone 8 Lit steady = System Fault
Zone 8 Slow Flash = Service Interval
Zone 8 Fast Flash = Ground Fault Condition
Press Cmd to return to the off state.
Issue
What is the 8 zone expansion module that is used on the DS7080IP32 control panel?
Solution
The EX8 would be the 8 zone expander module used to expand the DS7080IP32 panel. This expander wires on the keypad bus and can be addressed as 9-16 with no jumper (module address 101) or 17-24 with a jumper across pins 1 (module address 102), or zones 25-32 with a jumper across pins 2 (module address 103). You must use 9-16 first and power must be cycled after address changes for them to take effect.
Overview
RF3401 wireless point always shows an open state, will need to be reprogrammed in the normal state.
Issue
RF3401 wireless transmitter using the External contacts stays open all the time (no change of state).
Solution
Transmitter must be deleted and relearned with the External point in the NORMAL state.
Issue
An FA400 receiver that is disconnected will not force the keypad to display a missing message.
Solution
If two FA400 receivers are being used on the same D8125INV, the "Receiver Missing" message will not display if only one of the receivers is disconnected.
Issue
When attempting to connect to a DS7080iP-32 or DS7400Xi Ver4+ panel in WDSRP 2, Direct Connect does not appear as an option when Communicate is pressed.
Solution
WDSRP has not been set up to use Direct Connect function. Go to Utilities and Preferences, check Direct Serial Connect and press OK. Go back to Communicate screen and Direct Connect will appear.
Issue
How is the D6112 armed and disarmed?
Solution
Arming Your Security System
Your security system can be armed in many different ways, depending on the arming command used. Arming commands are those commands used to arm the system. The most basic arming command is to arm the entire system. This is done by entering your personal passcode and pressing ENT or by entering COMMAND 1.
To ARM your security system:
Enter your personal passcode and press ENT or enter an Arming Command. Your system may be programmed to send a "closing" report to the Central Station when arming.
Disarming Your Security System
Your security system is disarmed by entering your personal passcode and pressing ENT. When your system is armed, you must enter the premises through a designated entry door to prevent an immediate instant alarm condition. Opening the door starts an entry delay time and the Command Center emits a pulsing "beep" tone to remind you to disarm the system. Entering your personal passcode and pressing ENT before the delay time expires and the system will disarm. If you enter through a wrong door or fail to disarm the system before the entry delay expires, you will generate an immediate alarm.
To DISARM your security system:
Enter your personal passcode and press ENT. Your system may be programmed to send an "opening" report to the Central Station when disarming.
Issue
What type of RF receivers are compatible with the D4412/D6412?
Solution
The ITI receiver part number RF3226 and the Bosch receiver part number RF3224.
Issue
What do the command center warning tones mean?
Solution
Command Center Warning Signals
The Command Center contains a built-in sounder used as an interior warning device. A bell or siren can also be mounted on the exterior of your premises to alert your neighbors of an emergency and to give the police an audible reference to help them locate the alarm. Several different warning signals are emitted from the Command Center to alert you when an event occurs (not all signals will be heard outside). Some of these tones are optional, and can be selected by your alarm technician.
1. Entrance Warning: The Command Center beeps during the entry delay period to remind you to disarm your security system. If the security system is not disarmed before the entry delay expires, an alarm signal may be sent to the Central Station and the alarm audible sounds. 2. Keystroke Entry: Pressing any key on the Command Center sounds a short beep tone, indicating that the entry is accepted. 3. Faulted Zone: The Command Center sounder is activated for two seconds after you enter an arming command to indicate that a zone is faulted, and the indicator of the faulted zone lights. 4. Watch Tone: When the Perimeter Watch Mode is activated, the Command Center emits a brief tone to alert you when any perimeter zone is faulted and the zone indicator lights to indicate which zone is faulted. The tone sounds only when the door or window is opened. It does not sound again for that zone until the door or window is closed and then reopened. 5. Service Tone: Some zones may be programmed to sound a service tone when they are faulted. The zone indicator light annunciates which zone is faulted. To silence the service tone, enter COMMAND 4 or enter your personal passcode plus ENT, at the Command Center. NOTE: Some zones, such as fire zones, may be programmed so that the sounder cannot be silenced until the zone fault is corrected My system can be silenced by entering COMMAND 4 or by using my personal passcode plus ENT. The system cannot be silenced unless the zone is returned to normal. 6. Telephone Trouble: If the security system cannot report to the Central Station due to telephone line trouble or other cause, the Command Center emits a steady beep tone. This tone may be silenced by entering COMMAND 4 or your personal passcode plus ENT.
Issue
How to arm entire system with delays.
Solution
To arm the entire system with delays, follow the steps below:
COMMAND 1 is used to arm the entire system, both perimeter and interior zones. Once you have entered COMMAND 1, the exit delay time starts. You now have a predetermined amount of time to exit the protected area before the system arms. During the exit period, you may move through motion detectors or any protected area on your way to the exit door without causing an alarm. To cancel COMMAND 1, enter your personal passcode and press ENT.
NOTE: If you leave the building after the exit time expires, you may begin the entry delay, or initiate an alarm. If this happens, disarm your system by entering your personal passcode and press ENT . If your system reports to a Central Station, you may need to call them if an alarm occurs. Application
COMMAND 1 is useful in applications where you want your cleaning service, a serviceperson or anyone to arm your system when they leave, but you do not want them to have the passcode to disarm the system. COMMAND 1 arms the system, but it will not disarm the system.
Arming with COMMAND 1:
1. Ensure that all zones are secure. All of the Zone Status indicator lights on the Command Center should be off. 2. Press the COMMAND bar. The Command Mode indicator light comes on. 3. Press the 1 key. The PERIMETER indicator and the INTERIOR indicator lights begin to flash on and off. This indicates that the system has begun exit delay time. 4. To disarm your security system or cancel COMMAND 1, enter your personal passcode and press ENT before the delay time expires.
Issue
How can you arm the perimeter without delays?
Solution
Arm the Perimeter without Delays
COMMAND 2 is used to arm only the perimeter of your building, leaving the interior of the building disarmed. This command allows no exit or entry delay time through the perimeter, including the designated delay door. Although this command does not send a "Closing Report" to the Central Station, it will still send alarms. Enter your personal passcode plus ENT to cancel COMMAND 2.
Application
This arming command is useful in residential systems at night when everyone is home and ready to retire for the evening. In commercial installations, this arming command is useful when you are working late and you want the perimeter of the building armed until you are ready to leave. Arming with COMMAND 2:
1. Ensure that all perimeter zones are secure (interior zones are not armed with this command and may remain faulted while arming with COMMAND 2). 2. Press the COMMAND bar. The Command Mode indicator light comes on. 3. Press the 2 key. The PERIMETER and INSTANT indicator lights comes on. This indicates that the perimeter zones are armed without entry/exit delay time. 4. To disarm your security system or cancel COMMAND 2, enter your personal passcode and press ENT before the delay time expires.
Issue
Arming perimeter with delays
Solution
Arm the Perimeter with Delays
COMMAND 3 is used to arm only the perimeter of your building, leaving the interior of the building disarmed. Once you have entered COMMAND 3, the exit delay time starts. You now have a predetermined amount of time to leave before the perimeter arms. Although this command does not send a "Closing Report" to the Central Station, it will still send alarms. Enter your personal passcode and press ENT to cancel COMMAND 3.
Application
This arming command is useful in residential systems when you are leaving, but members of your family, a babysitter or a pet are still inside the house. In commercial installations, use this command to rearm your system when you are on the premises, but not yet open for business. This command will not send a "Closing Report" to the Central Station.
Arming with COMMAND 3:
1. Ensure that all perimeter zones are secure (interior zones are not armed with this command and may remain faulted while arming with COMMAND 3). 2. Press the COMMAND bar. The Command Mode indicator light comes on. 3. Press the 3 key. The PERIMETER indicator light flashes. This indicates that the system has begun exit delay time. When the delay time expires, the light remains steady. 4. To disarm your security system or cancel COMMAND 3, enter your personal passcode and press ENT before the delay time expires.