Issue
Trouble connecting to the D4412 with RPS / RAM IV using the DX4010i.
What dip switches need to be set to make the DX4010i connect to the panel?
What type of cable is needed between the DX4010i and the Laptop or PC?
Solution
RAMIV / RPS needs to be revision 3.6 or higher.
Set the address 0 (Installer's mode) Dip Switches 6 and 8 in the off postion on the DX4010i.
Use a NULL cable to connect the DX4010i to the Laptop or PC.
For remote programming connection, use the RJ-16 to molex connector to the Aux / Data header.
Lock the Installer or Reset Pin on the panel.
In the RSP/ RAMIV Connection screen change the connection type from MODEM to ENHANCED DIRECT, then click connect.
*If connected to a D4412 panel and the address is set wrong on the DX4010i then a message of "INVALID RAM PASSCODE" may be generated.
How to determine the max distance the DX2010 can be remote located from the control panel.
This distance is determined by whether or not the DX2010 is supplying auxiliary power to devices. The DX2010 has the capacity to provide 12 VDC at up to 100 mA from the Aux Output terminals to power external devices such as motion detectors.
When using the internal contacts on a FA210W, which mode should be selected ?
D8125INV,D9412,D7412,D7212,D9412G,D7412G,D7212G,D9412GV2,D7412GV2,D7212GV2,D9412GV3,D7412GV3,D7212GV3,D9412GV4,D7412GV4,D7212GV4,FA400
Issue
What are the proper steps to default a DS7100?
Solution
Enter program mode with a valid installers code #0 ( 98765 #0 ) is the default code. Or press and hold the S1 switch for 6 seconds.
Enter address 839#
Then press the S1 switch for 6 seconds.
Warning: Defaulting the DS7100 will erase all programming and user data in the system resulting in a system that needs to be reprogrammed.
Notice: This panal is equipped with Anti-Takeover Protection; all or part of the programmming may be locked so the program cannot be changed should someone attempt to take over the account.
How is a bypassed point returned to a normal condition upon disarm
D9412,D7412,D7212,D9412G,D7412G,D7212G,D9412GV2,D7412GV2,D7212GV2,D9412GV3,D7412GV3,D7212GV3,D9412GV4,D7412GV4,D7212GV4
How to configure the output in GV4 ver.2?
Default: 0
Selections: 0 to 8 (increments of 1)
Use this parameter to activate an output when the point goes into alarm.
The output does not activate for Trouble nor Supervisory events. Reset the output by clearing the memory from the keypad display.
The outputs used can be on an output module installed on either the Zonex bus or the SDI2 bus.
*Notice that the Relay will activate only when the point goes in to alarm, not when it changes to an off-normal state.
Follow the steps from this article to accomplish the BFSK relay functionality.