Step-by-step guide:
1. Determine which type of FPD-7024 hardware in use. There are differences in network communications programming depending on which type is in use (see figure 1).
Version 1.00-1.03 panel types are identified with words on panel keypads instead of Icons.
Version 1.06+ panel types are identified with Icons on panel keypads instead of words.
2. Obtain the following parameters.
Receiver IP Address and Port number.
Panel account number.
Supervision interval configured in central station’s network account for the panel.
3. The Number entry combines the receiver IP address and network supervision into a single location
4. Using the programming menu tree in figure 3 as a guide, follow the steps below to configure network communications in the version 1.03 or 1.06 panel type. Keypad Programming using menu tree
Press 0 followed by the installer code (default= 9876) to access keypad programming.
Save entries by pressing [ # ], or press star [ * ] to go back one level. Continue pressing star [ * ] to exit programing.
5. Determine the number entry according to the panel type in use.
Version 1.03 and earlier.
Use 300 second supervision both in the panel configuration as well as the network account at central station.
300 second supervision= Ack=15seconds, Poll=180 seconds and communication attempts=5 (the number of communication attempts is entered in a later step).
Combine the IP address and network supervision as described in table 1.
For example, enter the receiver IP address; 1 7 3. 8 4. 3 3. 8 2 as described in figure 4.
Version 1.06 and newer.
Determine the network supervision to be used in the panel and in central station’s network account (up to 24hours).
Combine the IP address and network supervision as described in table 2. The number of communication attempts is entered in a later step.
For example, enter the receiver IP address; 1 7 3. 8 4. 3 3. 8 2 using 24-hour supervision as described in figure 5.
6. Enter the receiver IP address and supervision interval.
Press 6-Program Accounts.
Press 1-PHONE/IP# 1.
Press 1-Number.
Enter the number from step 1.
Press # to save.
7. Enter the receiver Port number.
Press 2-PORT NUMBER.
Enter the receiver port number. For example, Port 7700 is entered as 07700.
Press # to save.
8. Enter the panel reporting format.
Press 3-FORMAT. Select a reporting format and press # to save.
0- DISABLE
1- 3/1 REPORT
2- 4/2 REPORT
3- BFSK REPORT
4- SIA, 110 RPRT
5- CONTACT ID
6- SIA, 300 RPRT
7- MDM 3A2 (Modem)
9. Enter the panel account number.
Press 4-ACCT NUMS.
Ver. 1.03 and earlier: Enter the 4-digit account number and press # to save.
Ver. 1.06 and newer: Enter the account number with leading zero’s, e.g. 0000001234 to fill all 10 digits.
10. **Version 1.06 only** Select IP MOD Primary.
Select 1 or 2 as described below for the address of the primary network communicator. This applies only when there are 2 communicators used for network communications. Note that only the
1-250 as Primary
2-134 as Primary
When a single network communicator is used, select 1 and address the communicator as 9 (option bus address 250).
When a second network communicator is used, address the secondary communicator as 6 (option bus address 134).
... View more